When is sprinkler protection required for a building column?
We have a New York City project with cast iron columns, and we're not sure of any code requirement that would address sprinkler requirements for protection of a cast iron column. Any help is much appreciated. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
17 Comments
Alex
6/7/2022 05:53:54 am
Hi,
Reply
Alex
6/7/2022 08:04:08 am
Update: I’m on the road now and thinking of this more. I have heard of rating the columns in storage applications but have never done so myself.
Reply
There are a couple examples of using side wall sprinklers to protect columns within fire protection standards. Some examples are NFPA 13 2013 16.1.4.1, NFPA 15 2017 7.4.3.4, and FM DS 7-32 2.2.1.4.6.
Reply
NW
6/7/2022 08:19:21 am
Only time I've ever come across using sprinklers on columns was for rubber tire storage. NFPA-13 2016 18.2 deals with it and requires it for steel columns not provided with fireproofing in certain storage arrangements.
Reply
Anthony
6/7/2022 08:29:45 am
Iron is considered non-combustible. It shouldn't require extra protection in any non-storage applications.
Reply
Franck
6/7/2022 10:40:48 am
It may be required to protect the columns when they are exposed to a combustible/flammable liquid fire, for example and could lead to a collapse of a roof or upper floors.
Reply
Todd E Wyatt
6/7/2022 08:41:40 am
The fire-resistance rating (FRR) protection of building elements (e.g. columns, beams, floor const, roof const) are required to have a FRR based on the building's Type of Construction. The FRR of assemblies (e.g. Fire Walls, Fire Barriers, Smoke Barriers, Smoke Partitions) are required to have a FRR based on the type of assemby it is.
Reply
Anthony Fuller
3/8/2024 09:51:52 pm
Thankyou
Reply
Zackery Geddies
6/7/2022 08:46:25 am
NFPA 409 Standard on Aircraft Hangars requires column protection in some instances. There also may be a local code requirement.
Reply
Rusty Scott
6/7/2022 09:41:02 am
The new-ish Savannah Ga JW Marriott Savannah Plant Riverside District Hotel has it's exposed columns in the museum atrium space protected with side wall sprinklers spaced approx. 10ft vertically. Have always meant to look up the codes behind it.
Reply
Franck
6/7/2022 10:44:03 am
If columns are already located in an adequately protected area, thyere is normally no need to protect them individually in addition.
Reply
Franck
6/7/2022 10:49:47 am
You can check, for example, FM data sheet 7.101 (free access on internet):
Reply
Franck
6/7/2022 10:50:35 am
Unfortunately, I can't add the sketch from the data sheet...
Reply
Colin Lusher
6/7/2022 11:24:24 am
Generally, protection of steel columns is required under certain storage arrangements. For instance, steel columns located in the middle of rack storage require some type of protection, either fire proofing or sprinklers. Likewise certain rubber tire storage arrangements require this. In bother cases, NFPA 13 allows for fireproofing in lieu of sprinklers.
Reply
Jack G
6/7/2022 11:42:48 am
IBC—- any year. Please review chapters 5 and 6 for its requirements of area/ building height and types of construction with“A”:being protected steel and columns and “ B “ being unprotected.
Reply
Paul Pinigis
6/8/2022 10:20:43 am
This refers to fireproofing of structural steel, not sprinkler protection.
Reply
Todd Wyatt
6/9/2022 08:57:27 am
Per IBC 2021, "TABLE 601 FIRE-RESISTANCE RATING REQUIREMENTS FOR BUILDING ELEMENTS (HOURS)" identifies the minimum fire-resistive rated (FRR) protection for "BUILDING ELEMENTS" including "Primary structural frame" which includes columns. The "A" and "B" in this table does not represent "protected" vs "unprotected" columns.
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop June '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
July 2024
PE PREP SERIES |