We are designing a barge loading/unloading slip. The product will be used motor oil. The barge slip will be protected by fire monitors. These will be supplied by a fire water pump house.
Due to space limitations, the pump house will be within a 50-ft radius of the corner of a barge (potential fire source). The pump house will enclose two diesel pumps and day tanks and will be sprinkler protected. Only three walls of the pump house will fall within the 50-ft circle. Question 1) NFPA Table 4.13.1.1.2 would dictate a 2-hour fire-resistance rating needed, but the IBC would lead you to believe a 1-hour rating is required. Can someone clarify which is required? Question 2) Do all the walls and the roof need to meet the rating? The simple solution would be to make everything a 2-hour rating. However, the pump house will have a 10'x10' door, roof hatches, and ventilation louvers. Placing these on the wall opposite to the fire source and outside of the 50 ft. circle would greatly simplify the design. Thank you in advance! Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
6 Comments
Chris Nelson
8/18/2022 08:19:39 am
4.14.1.1.2 calls out 4.14.1.1.3 which states:
Reply
Chris Nelson
8/18/2022 08:23:00 am
But to answer your questions
Reply
Franck
8/18/2022 10:40:14 am
The sprinkler protection would protect from a fire originating inside the pumphouse to possibly limit the damages.
Reply
Glenn Berger
8/18/2022 11:16:03 am
The IBC provides minimum requirements. NFPA 20 should be followed as it has more restrictive requirements.
Reply
Todd E Wyatt
8/19/2022 08:52:59 am
SHORT ANSWER
Reply
Patrick Nelligan
8/22/2022 12:22:04 pm
I understand everything above and special thanks to @Todd for the in-depth explanation. However, I have one question regarding Diesel Fire Pump Rooms in a fully sprinklered building. Since they must be designed to EH2 which requires a minimum 90-120 minute water supply duration requirement, should not the walls and ceiling meet those minimum requirements as well? Or am I missing something all together? I guess that is two questions. Thanks for you input.