We have a low-rise building with a manual wet standpipe and a sprinkler system. One combination riser is 6-inch and the other is 4-inch. Standpipes will be Class I.
The calculated sprinkler demand is 195 gpm (Light Hazard). My total manual wet standpipe system demand will be 750 gpm (500 gpm first riser + 250 gpm second riser). Does my fire pump need to accommodate the 750 gpm of the manual standpipe system, since they're interconnected? I know the fire department will handle the standpipe demand, but does the flow rating for the fire pump need to accommodate 750 gpm? I've searched but haven't found specific code references in NFPA 13 or 20 to address this sizing. Thanks in advance. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
9 Comments
Brett
7/3/2024 06:55:15 am
The idea behind a manual standpipe is that the fire department will provide the pressure required to operate the hose valves inside. You do not need to include any standpipe demand in your pump calculation. The pump is required to be tied into a manual standpipe, but it is not required to be sized to NFPA 14 design requirements.
Reply
Brian
7/3/2024 08:06:06 am
No, the fire pump is only for the sprinkler system. The fire truck is for the manual standpipe.
Reply
Josh
7/3/2024 08:10:05 am
On a manual standpipe system, the intent is for the fire department to use their pumper to boost the pressures at the FDC. What I do when I have a manual system is tell the FM what pressure is available in the standpipe after calculations so they know what they need to boost. You still have to account for 750 gpm in your manual calculations if you have 2 standpipes.
Reply
Pete H
7/3/2024 09:51:44 am
Yeah, that annex section hits the nail on the head.
Reply
Casey Milhorn
7/3/2024 08:17:52 am
As others have responded, no, the fire pump is sized to your sprinkler demand only, HOWEVER, you need to consider the path from your FDC to your standpipes independently, and size the feed main and standpipes by way of hydraulic calculation. You will use the responding fire departments pumper truck as your water source. Many designers will just plug in 165 to 175 psi static, with residual a pound or two less, and a supply at 750 gpm.
Reply
Glenn Berger
7/3/2024 08:26:25 am
I agree with the responses provided above.
Reply
Josh
7/3/2024 08:39:49 am
The OP does state it's class 1 just FYI.
Reply
Dan Wilder
7/3/2024 08:41:00 am
As it's always nice to see the backup
Reply
Jack G
7/3/2024 11:01:04 am
Dan nails it.