I am currently reviewing plans for a 6-story condominium project with two levels of underground parking coming up in Ontario, Canada.
The drawings show provisions for 42 electric vehicle parking spots (assuming a Level 2 charger included) in the underground parking garage. I have read the NFPA document on modern vehicles in parking structures and I was wondering if there any recommendations on what to look out for with the mechanical exhaust system or the sprinkler system designed for this particular area of the building? Stay safe, thanks. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
11 Comments
Dan Wilder
8/23/2022 07:56:17 am
Couple things come to mind for the sprinkler side:
Reply
Glenn Berger
8/23/2022 08:06:36 am
Need to ensure that the electrical design accounts that 100% of the chargers can be in use at the same time. Need to ensure that the charges are protected from physical damage.
Reply
Todd E Wyatt
8/23/2022 08:26:47 am
The National Building Code of Canada (NBC) calls parking garages “storage garages” and requires the following ventilation :
Reply
Franck
8/23/2022 09:14:33 am
You can also have a look at NFPA Journal – 2019 March/April issue – Ramp Risk (probably available through NFPA website).
Reply
Franck
8/23/2022 09:11:52 am
I would be very conservative for a new project.
Reply
Franck
8/23/2022 09:20:07 am
In addition to my above comments, electric vahicles have more problems.
Reply
Kostas Papapostolou
8/23/2022 10:12:02 am
Dear sirs
Reply
martin moffitt
8/23/2022 10:28:02 am
"Assuming?" do not assume anything, especially in a case like this.
Reply
Tim
8/24/2022 01:59:09 am
The fact is that a sprinkler system is likely not to extinguish a fire involving a EV. If that is the case and we need to contain fire to area of origin for extended period of time more than 60 minutes then perhaps a low density larger area approach must be considered. Similar to a Aircraft Hanger where cooling over exposure risk will prevent spread with sprinkler system not design to extinguish the original vehicle that ignited. Smoke control is critical smoke dilution with extraction shafts included if the space is underground or a basement.
Reply
Dale
8/24/2022 12:24:22 pm
I am currently working on a parking garage, that will utiize car stackers. The stackers will allow for 4 levels of vehicles. There is no current precedent, as NFPA only recently started covering 2 levels of stacked vehicles. We are treating this as a storage space. We are providing ESFR sprinklers at the roof deck, and creating a sidewall sprinkler system with the sprinkler located just under the floor of the stacker. We performed a calculation, having both systems included, to try to anticipate a real scenario.
Reply
8/30/2023 08:11:17 am
This blog post on Exhaust & Sprinkler Density for Electric Parking is an excellent read! The comprehensive insights provided about optimizing both exhaust systems and sprinkler density for electric parking spaces are incredibly valuable. The way the post delves into the technical aspects while keeping the language accessible is truly commendable. I appreciate how it not only explains the significance of proper ventilation and fire safety measures but also highlights their role in promoting sustainable and eco-friendly electric vehicle adoption. This is an informative and forward-thinking piece that offers practical solutions for a greener and safer future. Kudos to the author for shedding light on such a crucial topic with clarity and positivity!