For an entry lobby area that is open to the floor above with a elevator on the second floor, and there is a pitched skylight for the roof. Where do you locate the smoke detector for elevator recall? I could not find any specific requirements for smoke detector location requirements in NFPA 72.
What are the design/location requirements for a elevator recall smoke detector in this scenario? Note: This is a Daily Discussion question submitted anonymously to us. Submit a Question or Discuss This Here.
8 Comments
Chris
10/16/2017 08:13:16 am
This is an excellent question, and I come across it often. Please refer to NFPA 72, 2010 or 2013 edition, 17.7.3.1.3 and 17.7.3.1.4. This will lead you to the Annex which suggests, for ceilings greater than 15', you may mount the detector within 60" of the top of each elevator door opening to protect the opening. This is allowed because it is not being used for general detection, but rather, for the protection of the opening.
Reply
Chris
10/16/2017 08:40:30 am
I probably should have mentioned that this would be WALL mounted, although you probably gathered that already.
Reply
Connor
10/16/2017 05:00:11 pm
Yep I gathered it was to be wall mounted.
Jeremy
9/26/2018 09:09:42 am
Chris,
Reply
10/16/2017 10:21:43 am
How many floors does the elevator serve? More than just the main and "mezzanine" you indicated?
Reply
Connor
10/16/2017 05:02:20 pm
The elevator serves the basement, 1st and 2nd floors. The first and second floor entry area is the areas that are open to one another, and where the skylight is located.
Reply
Jesse
9/14/2021 01:21:04 pm
I have a similar situation where the ceiling above the elevator door is about 35' tall. In addition to the smoke within 60" of the elevator door, do I also need one at the ceiling for normal coverage?
Reply
Moderator
9/15/2021 10:19:35 am
Great question Jesse - we're going to re-ask this question in the forum as a new post so it gets logged and answered. Thanks for taking part in the Forum!
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop June '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
July 2024
PE PREP SERIES |