NFPA 20 is pretty clear on the orientation of the eccentric reducer on the suction (upstream) side of a fire pump.
But the diagrams seem to suggest that the diagonal slope (not the flat side) of the eccentric reducer is always on the bottom. Is this true even when the supply is being fed from above? For instance, we often have a stub into a fire pump room from the floor, then a vertical backflow preventer, then the feed comes vertically-down and to the fire pump. Which way is correct for the eccentric reducer when the feed is from above? Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
10 Comments
Pete H
7/9/2024 07:07:33 am
Pretty sure even if the feed is from above, you're still under guidance to put the flat side of the eccentric reducer. I think just being eccentric might be enough to reduce air pocket development. It still has to go 10 pipe diameters before the suction elbow which should get it to a horizontal feed.
Reply
Pete H
7/9/2024 07:15:23 am
"under guidance to put the flat side of the eccentric reducer on top" is what I meant to type in that first sentence.
Reply
Anthony
7/9/2024 07:35:13 am
If the feed is vertical it drops to a 90 then goes into the eccentric reducer. Don't put the eccentric reducer on the vertical drop with a 90 straight into the pump. Confirm with your pump rep if you need further guidance.
Reply
OP
7/9/2024 07:40:06 am
No the eccentric reducer wouldn't be on the vertical; it'd still be horizontal going into the pump.
Reply
Dan Wilder
7/9/2024 07:58:14 am
I've seen and done this before with the pump MFG & Rep approval....while not specifically called out in NFPA 20, this is allowable.
Reply
Glenn Berger
7/9/2024 08:15:42 am
With the eccentric reducer being placed in the horizontal piping supply to a fire pump, it is always flat on top.
Reply
Franck Orset
7/9/2024 08:37:20 am
For a very long time, I was pretty sure that the flat bottom was always on top (as it is the only drawing indicated in NFPA 20). And I discovered recently that I might have been wrong for several decades, as I found several other technical documentations stating that it was true only if the water was coming from the side or from below.
Reply
Franck
7/9/2024 08:39:51 am
https://www.linkedin.com/posts/danvolsky_check-your-pumps-eccentric-reducers-installation-activity-7084434651687075840--DVV/
Reply
Jack G
7/9/2024 10:33:03 am
This was discussed on the Meyer website 11/18/2020. 13 comments I believe.
Reply
Jack G
7/9/2024 04:49:34 pm
Another thing to consider are automatic air releases at the top of standpipes, and on individual floors of wet systems in addition to what’s required.
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop June '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
July 2024
PE PREP SERIES |