For a smoke control stair pressurization system designed in accordance with IBC 909 and IMC 513, does the code require a duct smoke detector on the supply fan?
Does the installation of a smoke damper at the stairway boundary factor into this requirement? (i.e. IBC 717.3.3.2 requires a detector within 5 feet of a smoke damper). Normally this motorized smoke damper is closed and then automatically opens upon activation of a specific fire alarm signal. NFPA 92 6.4.6.2 does require a duct detector on the stair pressurization supply fan; however, I'm unaware of a similar requirement in IBC/IMC. NFPA's intent is to detect smoke on the air supply and shut down the unit before smoke compromises the stairway. For elevator hoistways that require smoke control, IBC 909.21.4.2 states to provide a detector. I would have expected a general statement in IBC 909.12 with the same intention as NFPA 92; however, I do not see a similar requirement in the IBC/IMC for stairways. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
2 Comments
Todd Wyatt
6/4/2021 09:30:44 am
NFPA 92 (2018) is referenced by the 2021 IBC (https://codes.iccsafe.org/content/IBC2021P1/chapter-9-fire-protection-and-life-safety-systems) in 909.7 Airflow Design method and 909.8 Exhaust Method but is otherwise not referenced. Unless the jurisdiction (e.g. Building Official and/or Fire Marshal) has adopted the NFPA 92 by reference and/or other Codes (e.g. NFPA 101) that references the NFPA 92, this NFPA 92 requirement is not required.
Reply
Paul
6/4/2021 09:43:09 am
It is normally understood from IBC (2018 Edition), Section 909.21.4.2 that any smoke in the system shall shutdown the fan of the system.
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop June '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
July 2024
PE PREP SERIES |