I'm designing a fire suppression system for a new horse stables and barn. There is a hay loft above the stables, enclosed parking for farm vehicles, and a work area for food processing (mostly fruits).
The stables and hay loft are considered one space for fire suppression purposes. They will be heated (in-floor hydronics) to 10 deg C (50 deg F) so in theory, a wet system could be used. The heating system will use gas boilers connected to the local gas utility so I'm not too worried about losing heat. However, the stables will have barn doors around it (high infiltration) and the floors could be covered in hay/straw (reducing radiant heat from the floor). So - would a dry system still be a prudent choice even though the space will be heated? The project is in Southern BC, Canada. Our winter 1% design temperature is -6 deg C (21 deg F) but it rarely gets that cold. We currently use NFPA 13-2013. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
10 Comments
Anthony
8/15/2022 07:30:29 am
This can only be answered by the HVAC engineer (if there is one on this project) This is a heat transfer problem not a fire protection one.
Reply
Chris Nelson
8/15/2022 08:07:05 am
Anthony said it correctly. Ask your HVAC engineer. I just finished a project for a Fire Department where the apparatus bay is being heated by radiant floors and my hvac engineer couldnt promise that the space could be heated above 40F if the doors were left open so we went with a dry system to protect the system and the space.
Reply
Dan Wilder
8/15/2022 08:10:34 am
As Anthony said, this isn't our issue to confirm. The question to the owner is can the roof level fire protection system be maintained at or above 40°F (~4.5°C). While the floor may be heated, radiant transfer (or lack there of), loss through open doors, roof/wall level insulation, air currents...all play into those calculations.
Reply
Jesse
8/15/2022 08:18:14 am
All 13 says is that wet-system components must be kept at or above 40-deg F. So it really seems to be a questions for your HVAC guys. If they affirm that the system can be kept at 40-deg F or above go with a wet system.
Reply
Glenn Berger
8/15/2022 08:20:25 am
It appears that you have done due diligence and that the best solution is a dry pipe system, should not be a disputed point.
Reply
Gregory Merryfield
8/15/2022 12:21:35 pm
Agree with Glenn and Michael, Alex, et al.
Reply
Michael
8/15/2022 08:41:28 am
This is definitely a dry system application.
Reply
Albert
8/16/2022 09:20:42 pm
x2.
Reply
Dean Melanson
8/15/2022 08:42:23 am
There is no way the system could be guaranteed to be kept at the required temperature under the conditions described. While gas equipment is not directly affected by power loss, the pumps, automatic ignition and thermostat all need electricity to function. A dry system is appropriate.
Reply
Alex
8/15/2022 11:06:07 am
Hi,
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop June '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
July 2024
PE PREP SERIES |