Does NFPA 13 2022 Section 10.2.6.1.1.3 about "Vertical Change in Ceiling Elevation Greater Than 36 in." apply to all types of sprinklers? I have a contractor who argues that the paragraph does not apply to ESFR sprinklers. The design has a change in elevation of 14-feet and the last sprinkler on the high-bay side is 8'-4" feet horizontally from the vertical plane. Thanks for helping settle the disagreement here.
Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
7 Comments
Tim
4/20/2023 08:12:14 am
Chapter 10 is for standard uprights and pendents. Section 9.5 applies to ESFR except where modified by Chapter 14.
Reply
Brian Gerdwagen
4/20/2023 08:16:46 am
Perfect answer. Chapter 10 does not apply to ESFR.
Reply
Jesse
4/20/2023 08:25:46 am
He's right. This doesn't apply to suppression mode sprinklers.
Reply
Todd E Wyatt
4/20/2023 08:33:33 am
Tim is correct ...
Reply
James Evans
4/20/2023 08:37:51 am
In my book the sprinkler at 8'2" off the wall is over spaced. In too many situations there would be a rack at that elevation change either with this owner or with future tenants. It is always the best practice to space to that much of an elevation change no matter what the code indicates. This is not "good design".
Reply
Casey Milhorn
4/20/2023 02:23:43 pm
In laymen's terms the 3' elevation change rule is a common sense exception allowed for light and ordinary hazard occupancies only, and only up to 3'. Over 3' wouldn't be allowed for light and ordinary, so why would it be okay for storage/ESFR type occupancy or sprinklers? Activation time, the sprinkler activating nearest the heat source, and coverage are all issues at play here. NFPA many times says as much by NOT saying anything as to saying something. The intent of NFPA 13 is clearly to not allow what you have drawn in your schematic.
Reply
Panos
4/20/2023 02:24:47 pm
After a second look at the Standard, it seems to me that sub 10.2.6.1.1.3 is probably not the best subsection to justify that the specific design is not correct.
Reply