I have an 83,000 sqft total (3-story) Type II-B new construction building under the International Fire Code. Under IFC Table B105.1(2) I get a straight-table Fire Flow of 6,000 gpm at 4 hours. However, IFC Table B105.2 allows buildings with automatic sprinkler systems to have a "Minimum Fire Flow" of "25% of the value in Table B105.1(2)", and a "Flow Duration" of the "Duration in Table B105.1(2) at the reduced flow rate". With a sprinkler system, the Fire Flow becomes 1,500 gpm (= 6,000 gpm x 25%), that's pretty straight forward.
However, is the Flow Duration straight from the original reading of Table B105.1(2) (which is 4-hours) or is the duration taken from Table B105.1(2) at the new reduced Fire Flow Rate (lookup 1,500 gpm to get 2-hour duration)? In short, is a 83,000 sqft Type II-B building Fire Flow actually 1,500 gpm at 4-hours, or 1,500 gpm at 2-hours? Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
12 Comments
Alex Jenness
5/13/2021 09:04:35 am
Correct. 1500 GPM for 4 hours.
Reply
Darin Golden
5/13/2021 09:52:07 am
Table B105.2 is very clear that the required flow duration is at the reduced flow rate.
Reply
Colin Lusher
5/13/2021 12:04:10 pm
I don't think that is correct. It says "Duration in table B105.1(2) at the reduced flow rate". I interpret this to mean the original duration at the reduced flow rate. The duration is 4-hours, the reduced flow rate is 1500 gpm.
SLL
5/13/2021 12:27:14 pm
I agree. If the Flow Duration was the original duration, it would say 'Valve in Table B105.1(2). However, it reads 'Duration in Table B105.1(2) at the reduced flow rate'.
James
5/13/2021 12:41:22 pm
I don't have access to IFC Handbook, but is there any commentary around it that might clarify this?
Reply
Alex Jenness
5/13/2021 02:30:00 pm
I looked at the commentary and it didn't provide any more clarification, but table B105.2 already says to use the duration in table B105.1(2).
Reply
James
5/13/2021 02:35:54 pm
Right, but the real question is which duration?
Darin Golden
5/14/2021 01:42:04 pm
If the table intended to require the original flow duration it would simply state “duration in Table” like it does for non-sprinklered building. Why would it state “duration in table at reduced rate” if it meant the same thing.
Reply
Moderator
5/24/2021 07:45:09 am
Great discussion here - We're sending in a formal ICC interpretation request on this topic, and will post the feedback here when it comes in. Thanks for everyone's input on this!
Reply
Moderator
5/27/2021 10:33:35 am
Here is the submitted request to the ICC staff for an informal code interpretation:
Reply
Moderator
5/27/2021 10:34:22 am
And here is the informal response from ICC staff:
Reply
7/5/2022 11:45:29 am
Keep in mind not all AHJ's that use NFPA 13 or the IBC. Some do not use that appendix. as an Example NJ Fire Code requires an approved fire flow method by the Fire Official and references Land Use regulations in a Bulletin. Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop June '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
July 2024
PE PREP SERIES |