I have a project involving spray application of resin, and an exhaust system including multiple 60-ft tall exhaust stacks.
We are located in Ontario Canada, and the Ontario Building Code takes precedence. Any other codes cited need to be enacted by the OBC, or by a code enacted by OBC in order to be relevant. NFPA 13 is relevant here. Chapter 26 (NFPA 13-2019) includes material from other codes. Section 26.4 relates to Spray Application Using Flammable or Combustible Materials, and references NFPA 33. I have not found a reference in NFPA 13 that states that an in-duct sprinkler system SHALL be provided. It appears to me that Section 26.4 states requirements for IF a system is provided. Unless otherwise stated, are the requirements of Chapter 26 to be used in isolation, without enacting the full text of the other NFPA Code/Standard cited? If another NFPA Code/Standard is cited in Chapter 26, is the full text of the cited document to be followed? Where is the line drawn between the two documents? I have the NFPA 13 Handbook, and the supplemental text does not clarify this for me. Thank you very much for taking the time to read through this one.
9 Comments
Dan Wilder
11/28/2022 08:03:22 am
That section is provided IF an automatic fire protection system is used that falls into NFPA 13's purview (wet, dry, preaction..). The protection can also be water mist, dry chemical, CO2, or another gaseous agent.
Reply
Matt C
11/28/2022 08:48:30 am
In Ontario, it's Provincial Law. The Ontario Building Code is an Ontario Regulation that is enacted by it's sister Statute, the Building Code Act. Same goes for the Ontario Fire Code, just a different Regulation/Statute.
Reply
Corey Eppinghaus
11/28/2022 08:19:47 am
Have you not made your way to the Ontario fire code via the OBC? Might open up a way to get to NFPA 33
Reply
Corey Eppinghaus
11/28/2022 08:35:02 am
This should help
Reply
Matt C
11/28/2022 08:40:36 am
The OFC does not apply to the scope that is under permit - that's where the distinction between the Fire Code and the Building Code come in. Once you commission/occupy that portion of the building or piece of equipment then the OFC kicks in and the maintenance of the system can be enforced, either via manufacturer's recommendations or an applicable NFPA Standard.
Reply
Corey Eppinghaus
11/30/2022 10:23:08 am
The OBC references the OFC for flammable combustible liquids etc so the OFC would be applicable via Part 6 as the OBC has no requirements for spray booths
Todd E Wyatt
11/28/2022 08:41:50 am
ANSWER
Reply
Todd E Wyatt
11/28/2022 08:42:33 am
https://www.ontario.ca/laws/regulation/120332
Reply
Dwight
11/30/2022 10:19:16 am
I would be looking at the Ontario code that requires/regulates the installation of this exhaust system. I'm not in Canada, but in the US, it would be the mechanical code referenced by the building code.
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop June '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
July 2024
PE PREP SERIES |