We have a multistory hotel building with the rooms opening to an exterior corridor. There is Exterior Insulation Finish System (EIFS) along the walls of the exterior corridor.
NFPA 13 (2022), Section 9.2.3.3 allows omission of sprinklers from exterior exit corridors where the exterior wall of the corridor is at least 50% open and where the corridor is entirely of noncombustible construction. It seems from research that EIFS is considered combustible and would require sprinkler protection along the exterior corridor. Has anyone done more research on this or has this come up before for other projects with EIFS in the exterior corridors and ultimately required sprinkler protection? Thanks in advance. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
8 Comments
Jesse
6/14/2023 08:11:07 am
Oh the stories I could tell about EIFS...
Reply
Todd E Wyatt
6/14/2023 08:47:31 am
If the EIFS substrate is of “noncombustible, limited-combustible, or fire-retardant materials”, an automatic sprinkler system is permitted to be omitted per 2022 NFPA 13.
Reply
Todd E Wyatt
6/14/2023 08:48:12 am
REFERENCES
Reply
Todd E Wyatt
6/14/2023 08:49:00 am
REFERENCES continued ...
Reply
SCHULMAN
6/14/2023 09:34:45 am
In Europe you might get arrested for suggesting to omit these sprinklers .. Im with Jesse ... EIFS IS COMBUSTIBLE.
Reply
Pete H
6/14/2023 01:26:35 pm
No personal experience, but if it's combustible, you provide sprinkler protection. And it sounds pretty combustible.
Reply
Alex
6/14/2023 01:45:14 pm
My two favorite research projects back in school were both the Grenfell Tower and the Torch Tower (well.. fire 1 and 2!).
Reply
Kevin
6/28/2023 11:14:22 am
A question. Would EIFS system such as Dryvit EPS10 combustible foam with a flame spread rating of 25 or less per ASTM E84 would not require exterior/exposure protection? Regardless if an exterior corridor or just the entire wood frame exterior of 4 story apartment?
Reply