Is there an egress requirement for a garage structure that only houses the car stacker, with 10 bays and 3 levels?
What would a code path be for or against such a requirement? Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
8 Comments
Chad
4/25/2023 06:51:10 am
Its a "space" so yes.
Reply
Jesse
4/25/2023 08:10:50 am
From my time as the fire marshal for an AHJ, yes. Egress requirements always apply because its an occupiable space. Even presuming that only those with familiarity of the space will be within, a provision for their emergent egress must still be provided.
Reply
Todd E Wyatt
4/25/2023 08:45:24 am
SUMMARY
Reply
Todd E Wyatt
4/25/2023 08:45:44 am
REFERENCES
Reply
Chad
4/25/2023 08:57:38 am
Do you really think that the true intent and spirit of the code is to require 2 exit stairways from a mechanically parked car assuming travel distances are met?
Reply
Todd E Wyatt
4/25/2023 09:16:24 am
Most AHJs do not consider the minimum requirements for the Means of Egress as "totally useless" and will (generally) require the "most restrictive" requirements in this case.
Chad
4/25/2023 09:28:19 am
Who said the bare minimum was “totally useless”? I stated a specific and contradictory section was. And called into question the intent.
Reply
Glenn Berger
4/25/2023 09:44:23 am
Unless considered, confined space or similar, then then are egress rules to be used for all areas of all types of facilities.
Reply