I am designing a two-story dormitory Type II-B (under 2018 IBC) with CMU walls throughout.
The floor deck consists of 5-inch composite metal deck. The corridor walls and walls between suites must be 1/2-hour (due to sprinkler exception - NFPA 13 fully sprinklered). There is also a horizontal separation between the two floors of 1/2-hour minimum. There are two stair towers which are required to be 1-hour fire rated. With the walls of the stair tower requiring a higher rating than is required between the two floors, is the floor then required to also be 1 hour? In other words, can the floor penetrating a shaft enclosure (the walls of the stair shaft will sit on the metal deck) be of a lesser rating than the actual stair enclosure walls? From what I've read regarding continuity, I'd say the floor rating would have to be 1 hour; but, I'm not clear. Please help. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
5 Comments
Todd E Wyatt
12/13/2022 08:19:07 am
No, the “supporting construction” (e.g. 0-hour floor construction) for 1-Hour Fire Barriers (1FB) protecting Interior Exit Stairways (IES) and 0.5-Hour Fire Partitions (0.5FP) protecting the dwelling units are not required to have an equivalent 0-5 or 1-Hour fire resistance rating (FRR) per 2018 IBC 707.5.1 EX 2 (for FBs) and 2018 IBC 708.4.1 EX (for FPs).
Reply
Kharma Leonard
12/14/2022 08:40:44 am
Thank you so much for clearing this up. I will go back and read the references you have included in your response.
Reply
Glenn Berger
12/13/2022 09:20:24 am
The stair landings, if independent of the building structure does not require its own fire-rating.
Reply
Kharma Leonard
12/14/2022 08:41:22 am
Thanks for your response!
Reply
Joe Mueller
12/15/2022 09:14:01 am
Yes, if a rated Fire Barrier sits on a floor assembly then the floor assembly and supporting structural bay are required to have the matching rating. So if the CMU sits on the composite floor assembly, then the floor assembly and associated structural bay need to have a matching rating. See 2018 IBC 707.5.1. The only exception for not requiring supporting floor and structure is exception 2 for incidental use fire barriers in Type IIB, IIB and VB. The better option to have the CMU run continuously on the stair tower and not sit on the adjacent floor. You can chat with ICC about this, when I have, this is the opinion that I have be returned.
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop June '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
July 2024
PE PREP SERIES |