I have a 2 story hotel that is being converted to 13R apartments. The structure has filled block walls, and concrete slab ceilings on both floors. My question is about the seismic bracing. I have cored 5-inch holes for the 3-inch main that is to run the length of the building, through the block walls. The block walls are 12'-0 apart. Can the block walls be counted as lateral sway bracing? Or, do I need to place braces as usual, based on pipe weight? Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
9 Comments
David Kendrick
10/24/2022 08:32:40 am
Is seismic bracing required in 13R?
Reply
DW
10/24/2022 08:33:03 am
Unless your all thread rod is 6 inches or less, I don't see where you could omit seismic bracing. I would account for it if I had this scenario, and expect the AHJ to look for it. I'm not a seismic expert though.
Reply
Todd E Wyatt
10/24/2022 08:38:51 am
Hotels are classified as Group R-1 (Residential) Occupancy Classifications (OC). Apartments are classified as Group R-2 (Residential) Occupancy Classifications (OC).
Reply
koray uluc
10/24/2022 09:09:22 am
i don't think that such installation can be used as siesmic bracing, The block holes do not fix pipe tight because of required clearance between pipe and solid wall (minimum 2" bigger, for pipes under 4" diameter) to avoid pipe brakage during siesmic movements.
Reply
10/24/2022 09:16:26 am
Yes, Seismic/Sway Bracing is indeed required for NFPA 13R for those who asked the question above. Pipe hangers and bracing shall be per NFPA 13, which clearly requires sway bracing.
Reply
Randy Rathert
10/25/2022 09:00:42 am
I love the banter and reference to ( code) but it is a especially helpfull when the answers are backed by the actual section of code.
Reply
Colin Lusher
10/25/2022 11:32:22 am
Thanks for your opinion Randy. First, NFPA 13 and 13R are 'standards', not 'codes'. And second, when I provide a response to a question here, I'm looking to point the questioner in the right direction, not to do their homework for them. And third, if you're not bringing anything to the discussion, why bother with a snarky response?
Alex
10/24/2022 10:18:25 am
Hi,
Reply
Ryan Hinson
10/25/2022 11:51:48 am
First off, is seismic protection required per the applicable building code or ASCE/SEI 7?
Reply