We have an overhead ESFR sprinkler system under NFPA 13-2013 with K22.4 sprinklers.
There are ducts 14-inches to 20-inches in diameter that will be installed at 30-ft. What is the required separation distance for them to be considered separate obstructions where we can omit sprinklers below, as long as they are 24" away (horizontal) from the overhead sprinklers? Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
4 Comments
Pete H
5/23/2024 06:49:10 am
This got added in 2016 and isn't in 2013... but it answers your questions.
Reply
Glenn Berger
5/23/2024 08:19:10 am
There currently is no hard rule for separation of obstructions. For ductwork and lighting, the spacing that Pete mentions above can be considered a good rule of thumb.
Reply
Steve Cooper
5/23/2024 09:17:29 am
The three times rule would be what is applicable to this situation. 20" duct, you would need to be 60" away from the edge of the obstruction. Please always keep in mind the AHJ since there is sometimes wiggle room with much smaller obstructions if they don't impact safety of the system.
Reply
danefre
5/23/2024 10:22:00 am
Agreed with Pete.
Reply