Spray Room vs Spray Booth: When to use the requirements for one or the other?
I am working on a flammable spray application and was wondering if anyone has a any good metrics for when to determine if an enclosure is a "spray room" vs a "spray booth". I am working on a 40-ft by 10-ft enclosure which I would argue is a room, but NFPA 33 provides discernable direction even with Annex sections, especially with "this definition is not intended to limit the term spray booth to any particular design." This shows up in A.3.3.19. From NFPA 33 2021: Spray Booth 3.3.19 "A power-ventilated enclosure for a spray application operation or process that confines and limits the escape of the material being sprayed, including vapors, mists, dusts, and residues that are produced by the spraying operation and conducts or directs these materials to an exhaust system." Annex A.3.3.19: "Spray booths are manufactured in a variety of forms, including automotive refinishing, downdraft, open-face, traveling, tunnel, and updraft booths. This definition is not intended to limit the term spray booth to any particular design. The entire spray booth is part of the spray area. A spray booth is not a spray room." Spray Room 3.3.20 "A power-ventilated enclosure for a spray application operation or process that confines and limits the escape of the material being sprayed, including vapors, mists, dusts, and residues that are produced by the spraying operation and conducts or directs these materials to an exhaust system." Annex A.3.3.20 "The entire spray room is considered part of the spray area. A spray booth is not a spray room." Based on definitions there are no official metrics to determine when to use either definition. Is this perhaps a constructed room vs a manufactured structure? Thanks in advance. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
8 Comments
sean
7/4/2022 08:11:48 am
the building code has spray room as a fire rated room
Reply
Chad
7/4/2022 08:30:32 am
So that begs the question. If you build a 1 hour rated room to enclose a UL listed preconfigured spray booth, is the room a spray room?
Reply
Glenn Berger
7/4/2022 09:39:54 am
Do not let the similar terms get in the way of a correct design. IMO, the difference is pre-design (pre-approved) enclosure system, versus a built to suit (on-site) system with parts and pieces to achieve one's purpose.
Reply
Franck
7/4/2022 10:11:26 am
In a spray booth, the only activity is spraying and the size of the “booth” is limited to that area. A spray room is a room where you have spray application but is a bit larger and some area within the room not dedicated solely for that purpose.
Reply
Franck
7/4/2022 10:15:27 am
And as indicated by Glenn, a spray booth is normally manufactured for that purpose and installed on site, while a spray room is a room that has been designed on site for that purpose and adapted.
Reply
Chad
7/4/2022 11:16:02 am
So if you build a rate room closely around a spray booth…. When does it become a spray room??….. I have a tough time discerning when that happens
Reply
Assuming you are in a IBC jurisdiction, a "Spray Room" is determined by the building code:
Reply
Tom Reinhardt
7/5/2022 06:57:15 am
In my opinion a spray room .merely houses a spray booth. A room would have windows doors and rated walls. All not conducive to spray finishes. A spray booth is specifically designed for safe flammable spray finishes. Smooth surfaces, intrinsic lighting ,manometers etc.
Reply