Our project is a 16-bed hospice facility. The project site does not have a municipal water supply. The project is under NFPA 13, mostly Light Hazard, and an ancillary storage space in the basement is Ordinary Hazard.
We've designed a water storage tank which is buried outside. The discharge of the tank is approximately 5-feet above the suction side of a fire pump supplying the sprinkler system. I've designated the pump as a sprinkler booster pump and supplied power from an emergency MDP (main disconnect panel). The electrician is asking for a few details concerning the pump designation. Is the fire pump required to have a separate service with a dedicated ATS (automatic transfer switch)? Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
8 Comments
Glenn Berger
6/1/2022 08:08:57 am
ATS - not required unless multiple feeds are required in order to meet reliability requirements as set forth by the NEC and/or local AHJ.
Reply
Jesse
6/1/2022 08:24:16 am
Agree with Glenn here. Its an AHJ issue. An ATS isn't necessarily required unless the AHJ says so. But I confess I'm not really sure what you mean by pump "designation".
Reply
Todd E Wyatt
6/1/2022 08:29:24 am
2021 IBC requires the "circuits supplying fire pumps" to be protected in (1) of (4) methods :
Reply
Eric R
6/1/2022 08:43:23 am
Maybe someone can help me out here, cause my code searching this morning is drawing a blank.
Reply
Eric R
6/1/2022 09:00:41 am
Ok, think I found it, though it's not as detailed as I'd like.
Reply
sean
6/1/2022 08:43:43 am
Dedicated service is required for electrical fire pumps.
Reply
Darin Golden
6/1/2022 02:09:16 pm
Hi Sean,
Reply
Robert Bennett
6/26/2022 05:36:01 pm
Look at NEC section 695. Fire pumps have thier own section. Remind your electrical inspector and discus it with them prior to committing to a requirement. Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop June '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
July 2024
PE PREP SERIES |