We have a project where we're adding a sound (anechoic) chamber and and protecting it with clean agent.
A question came up as to whether or not dampers are required for the HVAC system that provide supply and return air to the pre-manufactured chamber. Is an anechoic chamber required to have dampers for limiting the migration of the clean agent? My thinking is that the clean agent will be activated by an air sampling system, so there should be no meaningful amount of smoke in the chamber. That said, do the dampers have to be listed for fire/smoke? Any help with getting specifics from code or a clearer understanding is always appreciated from the community so thanks in advance. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
8 Comments
Glenn Berger
2/20/2023 08:05:51 am
You want smoke dampers to contain the clean agent in the protected volume.
Reply
schulman
2/20/2023 08:07:27 am
to do the job for the clean agent system the dampers just need to stop the hole so you don't have pressure loss ... smoke/fire requirements would be for other code reasons such as wall rating or compartmentalization for egress ...
Reply
Jesse
2/20/2023 08:58:16 am
Determining the amount of agent needed requires a volume calc. So without the dampers, you would need to include the area beyond where the damper would be. Otherwise you agent concentration won't be correct.
Reply
Todd E Wyatt
2/20/2023 09:43:20 am
Per the scoping Code (2021 IBC), a “clean-agent system” (904.10) which is an “Alternative Automatic Fire-Extinguishing System” (904) is required to be “be designed, installed, inspected, tested and maintained” in accordance with 2018 NFPA 2001 Standard on Clean Agent Fire Extinguishing Systems.
Reply
Franck
2/20/2023 11:07:29 am
If you want to keep your gas concentration for at least 10 minutes, you will probably need dampers.
Reply
Chad
2/21/2023 08:47:15 am
Be careful if you provide sprinklers, they have to be installed upside down (water is to be delivered towards the cones, not inside the room).
Reply
Franck
2/20/2023 11:16:10 am
For the “overpressure” dampers, I have a “funny” real story.
Reply
12/26/2023 10:47:05 am
You need to imagine that your clean agent protected room is a large swimming pool that you are trying to fill up with water. Most clean agents like Novec 1230 (aka FK 5-1-12) or FM-200 (aka HFC227es) are heavier than air. The water and clean agent will leak out through all of the openings in the walls, doors, and floor. It will not leak out upward through openings in the ceiling. The HVAC supply and returns grills are at the ceiling and agent will leak upwards. If the HVAC is allowed to continue to run after agent discharge, you will dilute your extinguishing concentration. The best and easiest way to deal with that is to electrically interlock your clean agent to automatically shut down the HVAC upon agent discharge. You do not need dampers. Most of the time, HVAC shuts down instantaneously. If not, you can time delay the agent discharge to give time for the HVAC to shutdown. Keep in mind that if you have HVAC openings in walls or the floor, these will likely need to be dampered. Remember the swimming pool analogy.
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop June '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
July 2024
PE PREP SERIES |