Are sprinklers required to be controlled by valves which are physically located on the same floor level?
Are sprinklers in high ceilings OK to be controlled by valves on the upper level, or do they need to be controlled by a valve on the same level as the floor? A project with a second, or even third-story high ceiling in a lobby would be one example of this scenario. Another example could be an entrance to an underground parking garage with an NFPA 13 system. It makes sense for valves to control the sprinklers on the level the valve is on, just wondering about a specific code reference. I know about the exception for the top of stair shafts. Thank you everyone! Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
7 Comments
Dan Wilder
9/21/2022 08:13:04 am
Not to my knowledge, they just need to be labeled/identified as to what/where they serve and in an accessible/protected/heated location (8.3.1.8, 16.9.3.1.1, 16.9.3.4, 16.9.12.3 to name a few requirements, none say it has to be located on the same floor level)
Reply
Franck
9/21/2022 08:27:50 am
Not a requirement to my knowledge
Reply
Jesse
9/21/2022 08:50:43 am
Agree with Franck and Dan. Especially the part about knowing what level water is flowing on.
Reply
Glenn Berger
9/21/2022 08:55:47 am
As long as everything is documented, approved by the AHJ and owner's rep(s), the isolation valve does not need to be on the same level as the sprinklers. None of us know what you building con figuration is, such that we would only be guessing on proper location of sprinkler control valve.
Reply
Munny Khan
9/21/2022 09:06:13 am
I've found this issue in my recent new role with this small company where we take note of all issues of every job (where in my old role with a big company there were individuals for every little thing). I've found with this is the zoning set up for the fire alarm panel and the importance to have it as simple as possible. I'll admit I'm still not 100% comfortable with it but the owner is excellent with it, so I'm learning. I haven't questioned a code reference for it but it is something in another code or standard that is fire protection related and can contribute to a better overall life safety system in the end.
Reply
Alex
9/21/2022 09:07:40 am
Nothing in the code I can think of that requires isolations to be installed on the floor. My first thought is a parking garage where each dry system is installed within a single room. Just want to make sure its clearly delineated and the fire department knows how to isolate the system in the case of a false activation.
Reply
Todd E Wyatt
9/21/2022 09:23:30 am
SUMMARY
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop June '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
July 2024
PE PREP SERIES |