We have a project with an air supported dome structure. It's serving around 430,000+ sqft of indoor sports.
However, I am a bit confused with the type of construction this would be clasified as. As per NFPA 5000 and IBC, an air-supported structure can be Type II-B (000), but wouldn't we be limited on allowable floor area restrictions for the site of the building? Are there any exceptions to sprinkler protection for a building like this? I would really appreciate your point of view, thanks in advance. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
8 Comments
Pete H
6/16/2023 07:03:05 am
I don't know of an exception personally. Because I agree with you, by IBC standards (2020 edition), this is an A-4 occupancy (indoor sporting arena). It's assumedly to be sprinklered (you're asking this question on a fire protection forum), so I'd look at Table 506.2 in the IBC. Based on what I'm seeing: The allowable area for a sprinklered A-4 occupancy built out of type II-B construction is 38,000 sq. ft. Type I would be unlimited.
Reply
Dan Wilder
6/16/2023 08:09:05 am
NFPA 102 Section 9.5 would likely be helpful to allow some omission of sprinklers when over the field area (pending roof height) and over seating areas.
Reply
Glenn Berger
6/16/2023 08:16:02 am
The area over the stadium itself cannot be physically sprinklered. Most indoor (or covered) sports stadiums do not contain fire sprinkler systems in the arena area.
Reply
Jesse
6/16/2023 08:24:19 am
I'm going to reiterate what Glenn is saying. Its not feasible to protect over the playing field, and most sports facilities are like this.As an insurance guy I did assessments on several NBA arenas and they are, but more to protect the cat-walks and scoreboard / jumbo-tron things
Reply
Todd E Wyatt
6/16/2023 08:58:31 am
SUMMARY
Reply
Todd E Wyatt
6/16/2023 08:59:15 am
REFERENCES
Reply
Todd E Wyatt
6/16/2023 09:00:15 am
REFERENCES continued ...
Reply
Ben Hoffmann
1/9/2024 03:44:28 pm
Check IBC Section 507 Unlimited Area Buildings, specifically Section 507.4, Sprinklered, one-story buildings, Exception 2 where automatic sprinkler system shall not be required in areas occupied for indoor participant sports provided you have direct egress to the outside, have a fire alarm system, and have sprinklers in the ancillary / non-sport areas (storage, locker rooms, etc.)
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop June '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
July 2024
PE PREP SERIES |