A non-combustible building has an 8-ft high space above an acoustic tile ceiling with a 30-inch wide expanded steel catwalk that is accessible from a stair shaft by a locked door.
The space is congested with building services, such as ducts, cables, and cast iron plumbing. Does the NFPA 13-2019 9.2.1.2 exception apply? NFPA 13-2019 9.2.1.2 (8.15.1.2.2 in 2016) Concealed spaces of noncombustible and limited-combustible construction with limited access and not permitting occupancy or storage of combustibles shall not require sprinkler protection. Thanks in advance. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
8 Comments
Dan Wilder
11/22/2022 06:50:53 am
Unfortunately, the door and the catwalk make it accessible, no different than a mechanical room. Locked doors do not qualify an area to be limited access, having to remove a ceiling tile or even possibly an access panel. The other aspect is the "not permitting storage"...catwalks are ripe with air filters and boxes of stuff that need homes.
Reply
Anthony
11/22/2022 07:15:26 am
Totally agree with Dan here. Catwalks and walkable ceilings are becoming more common place especially in industrial settings and require sprinkler coverage.
Reply
Todd E Wyatt
11/22/2022 08:15:41 am
The "catwalk" condition you describe are defined by 2021 IBC as "equipment platforms" (EP) and are defined as follows :
Reply
Adam
11/22/2022 08:45:15 am
I'm wondering about the 'occupancy' statement. Does strict maintenance work qualify as occupying the space?
Reply
Glenn Berger
11/22/2022 08:48:09 am
Exception does not apply, since a door is provided. The fact that a platform is provided also works against you in trying to use the exception.
Reply
Alex
11/22/2022 09:08:50 am
I agree with others above, since a door is provided, I would not consider this a concealed space.
Reply
Jesse
11/22/2022 09:56:16 am
The door is the downfall. It needs to be protected.
Reply
Robb K
11/22/2022 07:50:31 pm
I have same issue... I am on a project with a larger ceiling space with catwalks - above a corrosion repair hangar and only accessible by a man-ladder with an OSHA cage - USNavy NAVFAC just demanded heat detection in this space inlieu of sprinklers - which seems wrong. I am the Eng Tech and argued against my FPE DOR, as he accepted this. everything is noncombustible - accept for mayber wire insulation and fan belts. So I told the prime contractor - the government needs to pay additional as this is not required by the code, am i wrong?
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop June '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
July 2024
PE PREP SERIES |