What is the most appropriate Commodity Classification for wood chips (used for grilling) and wood mulch (used for pet bedding)?
The packaging consists of sealed paper bags that are palletized and secured with stretch wrap (plastic film) to stabilize the load onto the pallet. My initial thoughts would be a Class III Commodity, but NFPA 13 2019 Table A20.4(b) mentions "wood patterns" as being Class IV. I'm not certain of the definition of "wood patterns". Your input and wisdom is much appreciated. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
7 Comments
Glenn Berger
7/28/2023 08:14:10 am
An argument can be made for various different type of commodities. Be careful of the plastic film wrapping in the analysis of storage material.
Reply
Dan Wilder
7/28/2023 08:39:51 am
Wood (lumber), wood chips, charcoal (basic)... all fall into Class III (13-22' - 20.4.3 + Annex)
Reply
7/28/2023 08:44:28 am
20.4.3.1
Reply
Anthony
7/28/2023 08:45:33 am
Sounds like palletized, class 3, encapsulated.
Reply
Pete H
7/28/2023 09:08:49 am
I'd go class III.
Reply
Dave
7/28/2023 11:34:12 am
I have always assumed "wood patterns" were the library of wood master pattarns used in creating the sand molds in the foundry industry..
Reply
Franck
7/28/2023 12:01:08 pm
I would go to class III (and then possibly add penalties for packaging. pallets as indicated above).
Reply