I am planning a sprinkler system for a warehouse which is in a seismic area. Because of the ceiling structure, we need to use trapeze hangers, and possibly combine it with the seismic bracing. We are planning to use steel angles attached to concrete purlins, based on the sketch below, and put the seismic bracing to this steel angle (like we usually would do with a trapeze hanger). Is something like this allowed?
Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
8 Comments
Dan Wilder
7/8/2022 07:45:45 am
This would be a question only a structural engineer can answer. The lateral & lower shearing/twisting forces hitting that lower purlin are a big question along with sizing of both the angle iron and the attachment hardware to/through to the purlins to the adjacent secondary structure.
Reply
Glenn Berger
7/8/2022 08:11:33 am
My gut reaction is that this would not be allowed.
Reply
David Kendrick
7/8/2022 08:31:11 am
NFPA 13 is published with the engineering using best available technology and consensus of the industry for product application.
Reply
James Phifer
7/8/2022 08:41:28 am
I believe NFPA 13: 9.3.5.1.4 (2016 ed) addresses this but you would need to prove the angle iron is capable of meeting your seismic needs.
Reply
David Pitts
7/8/2022 08:47:53 am
Looks like you would be better off attaching the seismic bracing directly to the concrete tee with a Hilti Kwik Bolt. Like Dan Wilder said this would be a question for the structural engineer.
Reply
Cliff Schulze
7/8/2022 08:58:29 am
I would be concerned about drilling through the bottom of a concrete joist like that. I've worked on projects where they wouldn't let us connect to the bottom third of a concrete joist because that's where they have rebar installed.
Reply
Ryan Hinson
7/8/2022 09:33:50 am
While your approach would appear to be feasible, as previously stated, you are now in the structural engineering realm. I would also wonder the following:
Reply
Anthony
7/11/2022 08:56:28 am
Per NFPA 13-16 9.1.1.3.1 and 9.3.5.1.4 you can in fact use the same support for both sway bracing and gravity load support.
Reply