In my area many designers use the main test/drain or one of the FDC inlets to conduct forward flow for the double check backflow assembly. They use the velocity pressure pitot equation to demonstrate that they will achieve the system demand flow. During the acceptance testing, I verify that the system demand is achieved by measuring with a pitot gauge and calculating the flow.
I generally use a coefficient of 1 when a hose monster or the main drain piping is flowed from, because they are long runs of smooth continuous pipe. Is this appropriate or should I be using some other coefficient? Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
6 Comments
Alex
10/5/2021 05:18:25 am
Hi Anonymous,
Reply
Jesse
10/5/2021 08:10:27 am
If its a Hose Monster branded device, they have coefficient data on their website.
Reply
Cordell
10/5/2021 08:30:11 am
In many instances the 2" main drain or a single 2-1/2" outlet will not achieve the desired flow rate. I have added a manifold with six 2-1/2" outlets to achieve the system flow. To answer your question regarding the outlet coefficient, a coefficient of 1 would not be suitable since this is not a smooth outlet. 0.9 or 0.8 would be a better option.
Reply
10/5/2021 10:38:56 am
As an AHJ, I agree with Cordell. The 2" main drain or a single 2-1/2" outlet will not achieve the desired flow rate. We require the installation of one to many 2-1/2" outlets to achieve the system flow.
Reply
sean
10/5/2021 07:08:32 pm
i think the main issue is 1 is a super efficient delivery a play pipe does not achieve that and it is significantly smoother and las more laminar flow a .9 is the max I would personally find acceptable.
Reply
Dan Wilder
10/6/2021 09:04:33 am
I recently had an AHJ redline a plan for this reason.
Reply