NFPA 1 and 13 exclude large storage containers of household goods such as those stacked within buildings by well-known brands.
We know the range of consumer plastics that should be expected within the containers. The containers themselves are made entirely of wood or of fiberglass with metal frame. They are stacked one atop another, as high as possible, inside buildings of storage occupancy. How are these hazards/commodities to be classified? Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
10 Comments
Jesse
5/5/2023 08:07:35 am
The post indicates you know the range of consumer plastic to be expected within the container. It would be helpful to know this range. 10%? 50%?
Reply
Casey Milhorn
5/5/2023 08:32:12 am
https://www.alamy.com/uhaul-ubox-storage-and-shipping-containers-furniture-and-household-packing-in-progress-image257496610.html?imageid=B6C064FE-24A7-49F3-B5E2-ABF45196C273&p=456410&pn=1&searchId=cd99f78167dd6db19ed6153961ec3c2d&searchtype=0
Reply
Casey Milhorn
5/5/2023 08:34:51 am
Let me amend that.... lol. Guilty of reading too fast and not far enough. SFPE suggests NOT using ESFR possible and going the route of a larger remote area (more sprinklers) and also increasing the hose allowance for outside manual fire fighting efforts.
Reply
Franck
5/5/2023 12:01:22 pm
You will probably don't like my answer.
Reply
Pete H
5/5/2023 01:08:53 pm
What household goods in large containers does NFPA 13 exclude?
Reply
Franck
5/6/2023 02:34:11 am
The issue is not the commodity inside, which will be covered by NFPA 13, but the fact they are stored inside large containers.
Reply
Barry L
5/5/2023 06:35:53 pm
We just did a warehouse with similar storage. We were really glad that it was for a nationwide company who employed a FPE to evaluate the commodity and prescribe design criteria. They did substantial testing. In addition to a pretty stiff CMSA design, we also provided a horizontal standpipe system per their engineering evaluation.
Reply
Marcel
5/8/2023 03:55:23 pm
Barry,
Reply
Aeman Narwal
12/13/2023 07:41:13 pm
Hi
Reply
Anthony
5/8/2023 07:32:16 am
Per NFPA 13-16:
Reply