Can a 4" pump with 4"-6" discharge fitting be used on a private 10" combination line (fire suppression and hydrants)?
NFPA 24 Section 13.1 states that no line less than 6" shall service a hydrant. But does the fact that NFPA 20 Section 4.16 allows the 4"-6" discharge fitting as part of the pump assembly overrule this? Thanks in advance. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
4 Comments
When are pressure reducing hose valves required on a dry automatic standpipe system?
I have a project where I have been asked to evaluate an existing sprinkler system for an 8-story apartment building. The original installation falls under NFPA 13/14/20 2013 edition. The building is served by four dry automatic standpipes and a separate wet sprinkler feed. The standpipes are not combination sprinkler/standpipes. The fire pump churn pressure is 212 psi and there is a pressure reducing valve provided for the wet system supply. There is no pressure reducing valve for the dry automatic standpipes. The hose valves on the standpipes are the pressure restricting type. Not pressure reducing. When reviewing the data sheets for the hose valves, it states "Adjustable restriction of pressures up to 175 lbs....at residual flow" but the valves themselves are rated to 300 psi. At normal, non-fire conditions, the standpipes have 23 psi static pressure of air, but if the dry valve were to trip for any reason, (non-fire or not) the standpipe exceeds 175psi static pressure on the 1st-7th floors. NFPA 14 2013 states that "7.2.3.2* Where the static pressure at a 21⁄2 in. (65 mm) hose connection exceeds 175 psi (12.1 bar), an approved pressure regulating device shall be provided to limit static and residual pressures at the outlet of the hose connection to 175 psi (12.1 bar)." Would the static pressure be considered the normal air pressure or the static pressure if the dry valve trips? My assumption here would be that the pressure restricting valve needs to be swapped for a pressure reducing type. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe I have a canopy that is completely detached from a building (school) and is an entirely a separate structure. The canopy has no walls and is not in an egress pathway. The canopy is used for bicycle storage and bicycles are not stored overnight.
Is there any code path to require sprinklers underneath this canopy? If not, what is the code path to omit fire sprinkler protection? Thanks for your help! Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe Are there any universal, non-AHJ-specific requirements for permitting sprinkler alterations and/or repairs?
I have been told that “code” requires a permit to be pulled for any and all sprinkler alterations. Upon further questioning, I determined that this came from a fire marshal showing my colleague something in the IBC once, but, even if that were true, wouldn’t that still require adoption and implementation by a jurisdiction? Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe Can window sprinklers be used to protect internal glazing in partitions in lieu of fire rated glass partition?
The life safety engineer has requested to provide sprinklers on internal fully glazed partitions to save the cost of fire rated glazed partition. Not for the entire hospital, only some internal partitions in a hospital for glazing with 1-hour fire rated ones. Although couldn't find anything in the NFPA 13 that support his request as I know this is valid only for atriums, am I right? I appreciate the help and response as always. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe I have seen this method of arranging fire suppression components (see attached schematic) several times where I live. The attached is a partial re-creation of the fire water entry schematic for a high-rise building with a fire pump. The system has low and high pressure zones. The underground parking dry systems are served by the municipal water directly, and the standpipes and aboveground sprinklers are fed by the pump. Questions: 1. Can you have a FDC serving the low pressure zones as shown on the suction side of the pump per NFPA-14 6.4.3.1? 2. If not, how should the schematic be arranged instead? 3. What could happen if the Low Pressure FDC were pressurized as shown? This project was built under the 2013 editions of NFPA-13, 14, and 20. I am asking because I am beginning design of a sprinkler system for a 22 story high-rise. Thanks for your help. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe What design considerations (if any) need to be taken into account for the new refrigerant changes that are coming up for the HVAC industry (slightly flammable or highly flammable refrigerants)?
Are there any code updates, guidelines reference materials etc. Would this possibly affect hazard classifications? Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe Can anyone make sense of extended coverage sprinkler max spacing and areas to me?
Looking at NFPA 13 (2016) Table 8.8.2.1.2 or (2022) Table 11.2.2.1.2 "Protection Areas and Maximum Spacing (Extended Coverage Upright and Pendent Spray Sprinklers): In unobstructed and obstructed noncombustible construction, the max spacing is uniform for 196 square foot protection areas as 14 feet. Kinda makes sense, 14 x 14 is 196. But then when we get to 144 square foot spacing for Ordinary Hazard, we have 12'-0" maximum spacing (okay, 12 x 12 is 144); but then when we do 144 square foot protection area for extra hazard or high piled storage on this chart, you can have 15'-0" max spacing. The way I'm reading it is: If you have 12' x 12' spacing in ordinary hazard, you can use the Extended coverage pressure for 144 square feet but if you have 10' x 14' spacing, despite a smaller protection area in ordinary hazard (144 sqft vs 140 sqft) because of the 14'-0" spacing, I should calculate using the head's starting pressure for 196 square foot area of protection starting pressure. Whereas the same situation in extra hazard or high piled storage would allow me to use the 144 square foot starting pressure, as I haven't exceeded the 15'-0" maximum spacing or the 144 sqft area of protection. Just seems counter-intuitive to me. Can anyone make this make sense? Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe Consider a high-piled rack storage area with 30 ft roof height and the following arrangements:
(A) Class I through IV and cartoned nonexpanded Group A plastic up to full rack height (B) Exposed nonexpanded Group A plastics, only up to five feet NFPA 13 Table 23.3.1 prescribes protection criteria for (A) as pendent K25.2 at 15 psi starting pressure; however, it does not provide protection criteria for exposed nonexpanded Group A plastics using K25.2 sprinklers where ceiling height is ≤ 30 ft. NFPA 13 Table 4.3.1.7.1.1 prescribes protection criteria for (B) as Ordinary Hazard Group 2. The owner will have exposed nonexpanded Group A plastics. They have agreed in writing to maintain exposed nonexpanded Group A plastic to the bottom five feet of the racks. Would storing exposed nonexpanded Group A plastics only in the lowest five feet of the rack, with Class I-IV above to the full rack height, be permissible? If so, the overhead sprinkler design under NFPA 13-2022 § 20.4.13.2 would only require the more-demanding of the two criteria (which is A), correct? Some have suggested that the presence of the exposed nonexpanded Group A plastic within the (A) criteria mixes with the (B) criteria to form a more hazardous condition than posed by either individual commodity / arrangement. However, NFPA 13 § 20.4.13.1 and 20.4.13.2 seem to require each commodity / arrangement to be considered independently and not to hypothesize protection requirements based on commodity / arrangement mixes. Long one, but thanks in advance. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe Is there a general rule of thumb concerning overall installation cost for standard coverage vs. extended coverage sprinklers?
That is, if I can use half as many extended coverage (EC) sprinklers, is the system going to cost significantly less or more? Two examples come to mind:
Thanks in advance. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe Hi All, I have a two part question regarding sprinklers below ductwork exceeding 48" wide. Both areas below (in different locations) are Ordinary Hazard, 130 sqft maximum spacing. When protecting below the ductwork in the elevation sketch below, is the 6'-11" dimension doubled to be 13'-10" the same as when spacing to a wall (SxL) ? Or can the distance to the next sprinkler be 15-ft (15 x 6-11 = 103.75 sqft)? In the plan view below, are sprinklers required below the 60" wide duct ABOVE the AHU (shown in green), if the vertical distance between the AHU and bottom of duct is greater than 24"? This would be under NFPA 13-2019, Section 9.5.5.3.1.5. Many thanks!
Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe Does anyone know of a sleeve product that can be installed AFTER pipe installation without backing out the pipe?
The underlying issue is that I have a project with seismic requirements (for extra clearance at penetrations) that has many fire rated walls. Basic pipe sleeves with extra large clearance filled with fire caulk is our typical situation, but if a sleeve gets missed during rough-in, we're hoping to use something after that fact. So either looking for a split sleeve of some type, OR a way to fire caulk a 2 hour rated gypsum wall with extra large clearance per NFPA 13-2016 section 9.3.4.3. Thanks in advance. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe Hello everyone, I am currently working on a project where 5 deluge valves will be installed in a dedicate riser room. The room will only contain the deluge valves (5), the foam tank and air compressors.
How would you recommend I give dimensional requirements for this room to the architect? What's your thought process, or lessons learned, for sizing rooms like this? Thanks in advance - much appreciated. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe In a recent project, I asked for hydrant flow test results from the civil engineer, and I received Boundary Conditions instead.
Is there a way of using this information to validate hydraulic calculations? An example of Boundary Conditions given to us: Demand = 18.54 gpm (1.17 L/s), HGL = 463'-11" (141.41 m), Pressure = 64.1 psi (442 kPa). Thanks! Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe We have an existing manufacturing area subject to NFPA 13-2022 Edition.
The Ordinary Hazard Group 2 manufacturing area sprinkler system can meet Figure 21.2.2.3.2 requirements for 0.20 density over 2,200 SF plus 500 GPM for hose streams required for Class III storage to 20 ft. high. Does the Ordinary Hazard Group 2 requirement of Section 4.3.3.2 (2) still limit storage height to 12-ft, regardless, since this is not a dedicated storage area? Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe I am pricing sprinklers in a steel frame building with Z-Purlins and a white vinyl backed insulation composed of inorganic glass fibers which are bonded with a thermoset resin to form a uniformly textured blanket style insulation at the Roof.
In an otherwise noncombustible area above the ceiling will the White Vinyl Backed Vapor Barrier System now make this above ceiling area combustible, requiring sprinklers? From the data sheet I have found the vapor barrier has a flame spread of 0 but have found from a google search flame spread and combustibility are not the same. Thanks in advance. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe Good morning! Is there any NFPA 13 prescriptive option for this type of obstruction? These are ceiling waves with a horizontal fall chain lighting system. Thanks in advance.
Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe Can a branch line tee to multiple sprinklers? Please see the attached example. I'm trying to figure out if a branch line that has a tee to multiple sprinklers would then be considered a main or still part of the branch line. This question also applies to looped branch line systems. The classification of branch lines and mains can have a major effect on the amount of seismic bracing required.
NFPA 13 defines branch lines as "The pipes supplying sprinklers, either directly or through sprigs, drops, return bends, or arm-overs." NFPA defines arm-overs as "A horizontal pipe that extends from a branch line to a single sprinkler or a sprinkler above and below a ceiling." Therefore, others that I have talked to have argued that the branch line will become a cross main since it is now feeding two sprinklers off of one line. This as a result would require additional seismic bracing. NFPA defines a cross main as "The pipes serving the branch lines, either directly or through riser nipples." In my opinion, the pipe would remain a branch line because it still aligns with the branch line definition. Moreover, there is nothing in NFPA that says that branching/teeing from a branch line automatically reclassifies the branch line as a main. Just because a pipe is no longer serving as an arm-over doesn't categorize the pipe feeding it as a main. The distinction between branch lines and cross mains is primarily based on their roles within the overall system, branch lines serve individual zones or areas, while cross mains supply multiple branch lines. What do you think? Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe Are air compressors for dry fire sprinkler systems required to be listed?
Thanks in advance. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe I am a President of Board of a 4-story condo building. The building was built in 1982 and is concrete block.
We received permission from fire marshal several years ago to remove all our fire hoses. The fire department told us that if there was a fire they would not use them. They would hook up to the FDC in front of our building. My question is - what is the purpose of the building's fire pump, and can we petition to also have it removed? What are the deciding factors or requirements on when a deluge system would be required on a stage to separate the stage from the audience?
This would be for the proscenium opening protection. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe Does code allow a fire sprinkler riser to be installed in a rated stairwell enclosure?
Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe Is "tenting" wet system piping (in an unheated attic) an appropriate approach to protect the pipes when the outside air temperature can drop to approximately 0 degrees F for multiple consecutive days?
In this case, the soffit and ridge vents allow exterior air into the attic space and there is no air barrier to prevent cold air infiltration. I have reviewed NFPA 13 and 13R and cannot find a definitive answer. Many thanks for assisting. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe For multi family buildings, I am being told that for a 4-story building, normally the fire pumps are only 15HP because the standpipes are pressurized by the fire trucks.
My understanding of NFPA 20 is that it would still be required to have a correctly sized fire pump without considering the size of the pump on the local fire trucks. Is this an industry norm that is allowed by certain AHJ’s or is there code related to multi family that I am missing? Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe Hello, First post for me here, thanks in advance for the assistance. In regards to the irregular room and spacing off the walls, I understand the .75 allowance up to 11'3" for the irregular or less than 90 degree wall (NFPA 13, 2019, 10.2.5.2.2). However, I have a set of plans I'm reviewing showing four rooms with only one sprinkler and they are applying this section as one wall in each room is irregular - however - the other walls are all regular 90 degree walls but they are exceeding 7'6" off those walls as well. In my interpretation, they should only be able to apply the above section for the irregular walls only, not normal 90 degree walls. In this situation I would request an additional head in each room. Am I missing something here? Thank you.
Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop June '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
July 2024
PE PREP SERIES |