Is there anything in NFPA 13 that forbids multiple pipes (two, in this case) being supported by a single trapeze?
Assumption here would be that the trapeze has been accurately calculated to support the combined weight of the two pipes (per NFPA 13 Chapter 9, 2016 Edition). Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
5 Comments
Mike
8/2/2021 08:20:41 am
Yes, it would be no different than hanging 2 pipes from the structure if it is adequately designed.
Reply
Jon Griffin
8/2/2021 08:27:50 am
Also, you only need to include a single instance of the 250-Lb. man-weight in your Trapeze calculation.
Reply
Dan Wilder
8/2/2021 08:30:49 am
I've done 4 in the past (increased the ATR and was using angle iron). Had to get structural sign off, put them well short of max spacing and placing them on Panel Points that were reinforced.
Reply
CJ Bonczyk
8/2/2021 08:54:10 am
Yes, you can. You have to do the math using the modulus in the back of NFPA 13. Once that is completed it is advisable to send the calculations and information over to a structural engineer for the project. We have had very odd requests by the structural engineer of record in order to hang from the structural with multiple lines above.
Reply
Alex
8/5/2021 07:43:19 am
Hi Anonymous,