I have a situation where I need to protect a modular home manufacturing facility.
It has a paint both that's self-contained with its own sprinkler hookups, all the regulars of a tiny home making shop basically. They will have rack storage of wood products up to 20' high and wanted the design to be such that they could move the storage rack locations in the future if they wished. NFPA 13 (2016) A.5.4.2 gives a list of some Extra Hazard Group 2 occupancies and it specifically lists (4) Manufactured home or modular building assemblies (where finished enclosure is present and has combustible interiors) I had made the assumption that ESFR was a worst case, safe bet design for the entire facility due to the amount of water you get from heads opening up. The contractor is concerned with how code says one thing in one place and something open to interpretation in another place. Section 8.4.6.6 says "ESFR sprinklers designed to meet any criteria in Chapter 12 through Chapter 20 shall be permitted to protect light and ordinary hazard applications." That's fine, but I just see that as just a statement. When you get to the requirements for Storage, Section 12.6.7.1 says the following: "ESFR sprinklers designed to meet any criteria in Chapter 12 or Chapter 14 through Chapter 20 shall be permitted to protect any of the following: (1) Light hazard occupancies (2) Ordinary hazard occupancies (3) Any storage arrangement in Chapter 13 referencing OH1, OH2, EH1, and EH2 design criteria" Item 3 is where I want to make the argument that we can in fact use ESFR sprinklers in an Extra Hazard Group 2 scenario. Can ESFR be used for an Extra Hazard Group 2 situation like this? I need some expert opinions/interpretations. Thanks in advance. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
13 Comments
Dan Wilder
2/8/2023 07:45:30 am
Hoping to learn from this one but my thoughts...
Reply
Glenn Berger
2/8/2023 08:14:30 am
In addition to the excellent statements made by Dan above, I recommend contacting various mfg of ESFR sprinklers as the allowable conditions do differ. With that said, you did not provide any information on the building construction for which you are protecting. That is another variable that needs to be considered.
Reply
Mike Morey
2/8/2023 08:16:57 am
As Mr. Wilder stated, the allowances to protect "occupancy group" designs with ESFR is limited to LH and OH. The later reference in the storage chapters is specifically for Low Piled/Misc storage and any other storage occupancy in the storage chapters that calls out an occupancy group protection scheme as being sufficient. Manufacturing and similar extra hazard facilities differ greatly in their fire loading and development and were not contemplated when ESFR was extended to protect other occupancies. As mentioned, LH and OH were added for ESFR warehouses with office, break, restroom, mechanical room, etc occupancies peppered throughout with and without ceilings to be protected without having to remove and replace ESFR sprinklers that would clearly put out a fire in those scenarios. It also helped ensure Shell/TI buildings were fully sprinklered at final inspection rather than owners trying to convince AHJs to accept wait and see on office shell areas etc.
Reply
Anthony
2/8/2023 08:29:21 am
ESFR isn't a better sprinkler it's a specific sprinkler. If NFPA 13 calls out EH2 specifically then you need to engage with your AHJ at a minimum. ESFR is specifically designed and tested for storage arrangements not open floor space and manufacturing.
Reply
Jesse
2/8/2023 08:34:40 am
ESFR is a completely different design approach. So whereas, NFPA 13 allows ESFR to be used in OH2 occupancy hazard class areas, its doesn't for EH.
Reply
Casey Milhorn
2/8/2023 08:54:11 am
I think I'm in agreement with everyone. If you are the EOR for this project, I would be hesitant to make the assumption that ESFR's are equivalent. If you are the fire protection contractor, I would DEFINITELY not make this leap.
Reply
Brad K
2/8/2023 09:00:32 am
Interesting question. One consideration when comparing OH/EH design density with ESFR calculations. Recall that Quick Response / Fast Response elements are not permitted for use with Extra hazard occupancies. Ref 2019 NFPA 13-10.2.3 and 19.3.3.2.2.2. Perhaps arguments can be made either way since 10.2.3 mentions density/area design method. This could become a sticking point in negotiations.
Reply
SAFPI Sebastian Stecyk
2/8/2023 09:12:27 am
In my opiniom, IT is not possibile.
Reply
JI
2/8/2023 10:37:42 am
While I think the advice here is pretty much on the side of ESFR protection and Extra Hazard are different hydraulic designs, I do have a recommendation.
Reply
Jonathan Worden
2/8/2023 10:43:53 am
Great question! Definitely learned something myself on this one. I, like many others probably immediately assumed more water = ability to protect higher hazard. It appears it's not that straight forward.
Reply
Sebastian Stecyk
2/8/2023 11:28:07 am
I found in NFPA 13 some additional information regarding use ESFR sprinklers in EX1 i EX2 hazard. You can also see point 14.2.7 and point 23.1.1 - NFPA 13, edition 2022,
Reply
Franck
2/8/2023 02:58:15 pm
ESFR are specific sprinklers (as indicated above) to suppress fire over a small area with storage occupancy.
Reply
Chris
2/13/2023 10:17:59 am
I agree with basically everyone else, ESFR's are only for storage applications, so if you have an area that isn't storage and is EH you cant use ESFR in that area, and I would say it also needs to be in a separate compartment from the ESFR's so you are not mixing SR with QR/FR.
Reply