Can we connect 2 or three buildings to the same fire alarm system? What about sprinkler?
What code basis (IBC or NFPA 13/72) would allow or disallow multiple buildings on the same system? Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
9 Comments
Todd E Wyatt
7/22/2024 08:26:33 am
Yes.
Reply
James Phifer
7/22/2024 08:38:03 am
A single fire sprinkler riser can be used to protect multiple buildings under certain circumstances.
Reply
Glenn Berger
7/22/2024 08:40:10 am
Are these buildings independent or separated by a distance?
Reply
Chad
7/22/2024 08:43:56 am
For fire alarm- Yes. Is it a good idea, IMO, no unless the AHJ has a fair amount of input/approval authority. A lot of local amendments will prohibit or restrict this.
Reply
Dan Wilder
7/22/2024 08:47:51 am
While I do not think there is any specific text (on the fire sprinkler side anyway) prohibiting this setup, it creates several issues/questions.
Reply
Dan Wilder
7/22/2024 08:52:47 am
and I should jump into Chapter 4 more often, thanks James!
Reply
Todd E Wyatt
7/23/2024 07:35:39 am
Yes, an automatic sprinkler system (ASPS) in one building is permitted to be supplied to a detached building where acceptable to the AHJ per NFPA 13-2023 4.4.6.2 .
Reply
Pete
7/24/2024 10:40:27 am
I would also consider how a wet system pipe running between the buildings would be protected from freezing if there is any distance between the buildings.
Reply
Mark Harris
7/24/2024 05:17:09 pm
I ran into this once and AHJ required separate water supply to a separate address even though buildings were connected. Had nothing to do with NFPA but was something in the IBC. As far as alarms again talk to AHJ as the fire department response will be based on how alarm is reported.
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop June '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
July 2024
PE PREP SERIES |