We have a hotel that is constructed with 12-inch TJI joists (composite engineered wood joists which have a continuous web, not an open web). There are gypsum ceilings attached directly to the bottom of the TJI joists. There is also at least 3.5-inches of insulation above the gypsum ceilings. Are we required to calculate 3,000 sqft or 8 residential sprinklers, or do we meet the noted code exception below? NFPA 13-2019 19.3.3.1.5.2(4) Item (10): Light or ordinary hazard occupancies where noncombustible or limited-combustible ceilings are attached to the bottom of composite wood joists either directly... , provided the adjacent joist channels are firestopped into volumes not exceeding 160 cubic ft, using materials equivalent to 1/2-inch gypsum board, and at least 3-1/2 inches of batt insulation is installed at the bottom of the joist channels when the ceiling is attached utilizing metal channels. What are the "adjacent joist channels"?
And does the construction we have equal the firestopping as noted? Does the gypsum ceiling attached to the bottom equal the firestopping, or is the firestopping something additional? Roland Huggins wrote a good article on this issue, but I'm still not sure. https://sprinklerage.com/sprinkler-protection-3000-ft2-modifier/ I have another senior tech convinced that this section is referring to an "unprotected" or non-firestopped combustible concealed space. Thanks in advance. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
10 Comments
Mike
9/28/2021 08:13:40 am
Fire stopping is blocking perpendicular to the joists. This is the fire stopping to limit the volume.
Reply
Alex
9/28/2021 09:48:25 am
Hi Anonymous,
Reply
Anonymoose
9/28/2021 01:41:07 pm
Reading that article it seems that you would need to put gypsum parallel to the joists to divide the spaces into 160 CF or less.
Reply
David
9/28/2021 04:48:49 pm
According to an NFSA interpretation (May 2007 #6) the volume must be calculated without taking the insulation into account. The NFSA expert of the day references intent sourced from previous editions of NFPA 13.
Reply
Anonymoose
9/28/2021 05:32:52 pm
Good to know, thanks!
David Kulbacki
9/29/2021 09:08:03 am
Looks like the 2019 edition cleared this up, and you can discount the volume taken up by the insulation. My mistake.
David Kulbacki
9/28/2021 04:52:11 pm
One thing to watch out for are the manner by which the joists are hung. I have seen quite a few joist hangers used that don't allow the joist to but hard up against the beams they are hung from. The result is that there is a gap where the joist meets the beam that will allow fire spread from joist channel to joist channel.
Reply
Mr. Quixote
9/29/2021 02:01:54 am
There is lots of confusion regarding this topic, but lets start at are sprinklers required within the TJI (Composite wood joists), assuming 13 code application of course.
Reply
David Kulbacki
9/29/2021 09:06:56 am
Looks like 19.3.3.1.5.2 (10) in 2019 edition would allow design area to not be increased.
Reply
RM Ballam
2/10/2022 10:55:51 am
The section requires 1/2" of gyp or equivalent. Most volumes created by composite wood joist are much smaller than the 160 cu stated in standard which means that the gyp bd. would only be required every 4th or 5th joist in most situations.
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop June '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
July 2024
PE PREP SERIES |