Which sprinklers are appropriate for kitchen fire protection?
What about in a hood versus near a hood? Thanks in advance. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
7 Comments
Anthony
10/5/2023 08:05:57 am
Any standard coverage sprinkler will be fine in a commercial kitchen. I personally like the concealed heads as they're often easier to clean, remain free of that grease dust build up that every ATC ceiling gets in a kitchen. Also they wont get knocked by the buss boy with a stack of hotel pans.
Reply
Glenn Berger
10/5/2023 08:13:53 am
Concur with Anthony fo sprinklers on the outside of the hood. Newer wet chemical system are equipped with a sprinkler connection that gets operated after the wet chem system is exhausted.
Reply
Dan Wilder
10/5/2023 09:16:29 am
Not sure about best, but best practice....
Reply
DS
10/5/2023 09:48:59 am
What about section 13:8.9 in the 2022 edition? This entire section is about Commercial-Type Cooking Equipment and Ventilation.
Reply
Fernando Katayama
10/5/2023 10:03:57 am
What about to use "MisteryHood" deep fat fryer sprinklers?
Reply
James Art
10/21/2023 09:25:37 pm
DS:
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop June '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
July 2024
PE PREP SERIES |