Are pendent sprinklers required below a decorative wood slat feature along the ceiling? Wood slats vary in height from 4" to 12" but is suspended at ceiling height (9'-0"). The area above the slats is concealed space and requires uprights. The total area percentage of slats is 42% below the concealed space. Thanks in advance.
Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
13 Comments
Pete H
9/15/2023 06:46:17 am
Can you protect this room with sidewalls?
Reply
Pete H
9/15/2023 06:48:27 am
Also giving it an extra few seconds, it doesn't look like 9'-0" is your ceiling height the slats are suspended from in that pic, it looks like 9'-0" is the height of the ceiling under the 12" soffit and the slats are suspended from the 10'-0" ceiling above that. Is this the case?
Reply
Pete H
9/15/2023 06:57:41 am
And finally to actually answer the question, yes you need to protect the floor under the wood slats,. If the above area is a combustible concealed space, you need to have protection at both levels.
James Evans
9/15/2023 09:11:59 am
You could not use sidewalls at 12" below the cieling because the soffit and the slats end at 12". This means your sidewall would need to be more than 12" if used on that wall with the soffit. Unless you sprayed from an adjacent wall opposite the slats. In situations like this we usually use a pend sprinkler on a bell reducer with no skirt or escutcheon and make the deflector about an 1" below the slats. the pipe can be painted to match the color.
Reply
DAVE
9/15/2023 10:40:28 am
Unfortunately, sidewalls can only be installed below smooth, horizontal, or sloped flat ceilings (LH) or smooth, flat ceiling where specifically listed.
Reply
Glenn Berger
9/15/2023 08:14:21 am
Your question states that the space above the slats is "concealed." Sprinklers would be required to protect the space below the decorative ceiling feature.
Reply
Anthony
9/15/2023 08:27:48 am
Yes, sprinklers are required in the habitable space if they're required in the combustible concealed space above..
Reply
Juan l
9/15/2023 08:28:28 am
Use EC Tyco side wall heads, and you don’t need any uprights.
Reply
Franck
9/15/2023 08:54:56 am
You have some requirements in NFPA 13 for open-grid ceilings. Which is what you have with your configuration.
Reply
Dan Wilder
9/15/2023 09:16:40 am
Are these slats attached directly to the ceiling?
Reply
SCHULMAN
9/15/2023 09:23:24 am
These guys are right, yes, you need sprinklers ... probably sidewalls are best but if it's an architectural issue and someone doesn't want sidewalls .. (I have done lots of crazy ceilings for lots of crazy bosses) ... you can put the sprinklers on pendants between some of the slats (making sure you have the floor coverage required at a minimum) and drop them to just "in-line" with the bottom edge of the wood slats which will help "hide them" - heck, I've even had contractors custom paint the piping and escutcheons etc... and as always - TALK TO YOUR AHJ.
Reply
Dave L.
9/15/2023 10:57:26 am
This one hits home. I've encountered a lot of variations on this as my architect friends keep coming up with new ideas. In some scenarios with multiple trendy baffles suspended from a ceiling above, I try to work with the architect to get them to suspend the slats low enough from the ceiling so they do not affect the spray pattern. I just had some projects that had areas similar to the posed question where they are attached directly to the ceiling. Sidewall sprinklers cannot be used below this type of ceiling (8.4.2 '16 ed; 10.3.2 '19 ed.). I was able to talk the architect into allowing me to extend 1” drops to pendent sprinklers centered between two slats, deflector just below the slats, let the architect choose the sprinkler color, and paint-out the pipe. Sprinkie made a mock-up to show the architect. They chose painting the pipe over that over a long escutcheon (that us old timers have a nickname for). In my case, the deflector of the pendent was able to be at 12” below the ceiling, although I suppose this could be treated as obstructed construction and go up to 22”. The space above the ceiling is its own situation.
Reply
AM
9/20/2023 03:23:39 pm
If the slat has no backer then we would follow open grid ceilings and protect with uprights, spacing dependent on deflector distance above top of baffle. If the slat has a finished backer and all ceilings return to the deck we would place the pendent at 12" below the finished backer with no uprights above 225sf spacing. If the slat has a backer but all ceilings do not return to deck we would protect above and below 225sf spacing.
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop June '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
July 2024
PE PREP SERIES |