Are flexible couplings required at riser for vertical support?
My project has a vertical support for a 30-ft long 6-inch riser. I used a riser clamp with two wall-mounted welded brackets to provide vertical load hanger at about 20-ft AFF. The inspector commented that I have to provide a flexible coupling above and below within 24" of the point of attachment. His reasoning is: 18.2.3.1(6) NFPA 13 2022 edition (6) Within 24 in. above and 24 in below any intermediate points of support for a riser or other vertical pipe. Anyone has suggestion for better way to put a vertical support at the riser? Is one ATR hanger at the top of the riser sufficient? Thanks in advance. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
10 Comments
Jim Phifer
9/19/2023 08:22:41 am
You didn't state if this project was located within an earthquake zone.
Reply
Jesse
9/19/2023 08:31:23 am
Is your project in a seismic zone.
Reply
Todd
9/19/2023 08:45:34 am
What is the building's Seismic Design Catagory?
Reply
Brad K
9/19/2023 09:02:09 am
Addressing the top of riser bracing. If Seismic is required, 13-18.5.8 (2019) shall be provided with a four-way brace.
Reply
Inspector
9/19/2023 09:12:00 am
I have to say as an inspector, I think this is a good catch. I understand that it may be inconvenient, but having that much vertical pipe above and below that support could cause a lot of pressure at the support if the building/sprinkler system were to shift back and forth. Even if the sprinkler system is braced throughout, the wall where your support is on the riser could move independently of the sprinkler pipe and cause an issue. Limiting the movement of the pipe could cause it to break disabling the entire system.
Reply
Dan Wilder
9/19/2023 09:43:43 am
The first question is a little confusing (couplings don't provide support), so I am reading it as "Are flexible couplings required on a riser at the point of vertical support". This is also assuming this is a seismic application but since soo many AHJ's apply riser requirements to non-seismic areas, any reference from Chapter 18 technically should not apply.
Reply
DAVE
9/19/2023 01:10:14 pm
^^ This.
Reply
James Art, FPE
9/20/2023 10:42:50 am
SOME FLEXIBILITY:
Reply
Luis
11/21/2023 02:47:20 pm
So if I have a riser in a vertical pipe chase, without floor penetration or offsets, and I support it via brackets anchored to a wall, for example, every 10ft, I would need to place 2 flexible couplings near each bracket?
Reply
Luis
11/21/2023 02:48:44 pm
(Assuming it is on a high seismic area)
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop June '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
July 2024
PE PREP SERIES |