I got asked a weird question about NFPA 13 requiring sprinklers to be readily accessible.
A co-worker told me they didn't believe some sprinklers that would installed in a mechanical room we're designing would be easily accessible post-construction and asked if there were any kind of access requirements. I can't think of anything in NFPA 13 that would require every head be easily accessible in the same way that NFPA 72 requires certain fire alarm components to be readily accessible. Is there a requirement that sprinklers be accessible? Where does this stem from? Thanks in advance. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
9 Comments
9/4/2023 08:58:26 am
Sprinklers are required to be visually inspected periodically so visual capability is required. They therefore cannot be hidden from sight. You could technically accomplish visual inspection with a camera. In a sprinkler operates, access to it to replace it will be required so design should take that into account but it is not required. If one needs to remove ductwork, conduit, or anything else to get to it, it is still technically accessible.
Reply
Glenn Berger
9/4/2023 11:10:41 am
NFPA 13 provides guidance on obstructions. NFPA 13 provides guidance on testing / inspection.
Reply
Robert W Hughes
9/4/2023 12:08:14 pm
No
Reply
Dan Wilder
9/4/2023 02:00:00 pm
NFPA 13 only requires valves to be accessible and sprinklers for specific systems be accessible (duct sprinklers for example).
Reply
This article sums up the testing:
Reply
Juan L
9/15/2023 08:37:57 am
Excellent explanation, just one comment;
Reply
Pete H
9/5/2023 06:28:53 am
As many sprinklers can be in inaccessible combustible concealed spaces: Not at all.
Reply
10/31/2023 06:09:07 am
The post's material is both substantial and easily understood. It addresses potential issues and concerns that may emerge during construction or renovation by providing a comprehensive explanation of the regulations controlling the accessibility of fire sprinkler systems. There is a clear structure and organization to the content. The dedication to safety and the post's adherence to fire safety rules are two of its strengths. It highlights the need of having readily available and operational fire sprinklers to protect people and property.
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop June '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
July 2024
PE PREP SERIES |