Has anyone designed a dry manual standpipe for a pier or dock standpipe system in the past?
My question is in regards to materials used for the pipe. With the tides rising and falling my client is struggling to find an approved material that will allow for enough flexibility. I walked an adjacent marina to our project and it looked like they used 4" heavy-duty rubber tubing to run out the standpipe lines and transitioned to steel only for the vertical 2 1/2" up to the hose valves on the dock. Any information to point us in the right direction would be helpful. Thanks in advance. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
11 Comments
David Kendrick
6/6/2023 08:12:20 am
Metraflex
Reply
SCHULMAN
6/6/2023 08:19:20 am
NFPA 14: 4.2.6 says you can use any pipe as long as it is installed within the limits of its listing and per the manufacturer's instructions. So if it meets the pressure requirements and is installed correctly and passes tests you should be good. The rubber tubing sounds like a good idea for the use. Talk to your AHJ / Fire Marshall ... Best of luck
Reply
Dan Wilder
6/6/2023 08:25:19 am
While I have not designed one, what I've seen in the past:
Reply
Pete H
6/6/2023 08:53:37 am
Seeing the metraflex mentions here, I'll just mention that Reliable just dropped their equivalent "Rascoloop"
Reply
Joe F
6/6/2023 10:00:05 am
We have designed and installed a few in the past. We typically used SCH-80 PVC, and installed the piping between the dock joist below the deck boards to protect from physical damage, and sun damage over time.
Reply
Pete D.
6/6/2023 10:33:59 am
I would analyze the buoyant force acting on the pipe. I like the idea of using metraflex, but those are expensive.
Reply
Ryan Hinson
6/6/2023 12:30:53 pm
Be careful about use of HDPE (or any plastic pipe) in aboveground installation for FP as it is not listed for such use. Nor is any plastic listed in NFPA 14 (2016) Table 4.2.1 or for above ground installation per NFPA 24.
Reply
Colin Lusher
6/6/2023 01:13:21 pm
I've designed these for fixed piers in Hawaii, and we've used all stainless steel pipe and fittings. I'm not sure about the flexibility issue with your moving dock, but we used a metraflex at the point of connection from the pier to the land.
Reply
Scott Chambers/Champion fire design
6/9/2023 10:12:12 pm
I have run a few horizontal standpipes above and below a pier. Above we used galvanized and stainless steel with grooved ends. Below the pier was a bit more challenging both for corrosion resistance and durability from rising waters and the waves constantly crashing against it. Cement lined ductile iron pipe with flanged ends was found to be most durable. Of course securing it to the pier also plays a huge role in its longevity. They now make quite a bit of plastic and epoxy coated hanging materials which wouldn't be a bad idea to use. Good luck.
Reply
Shane Gilbertson
6/12/2023 12:49:37 pm
Following for ideas.
Reply
Patrick Drumm
11/24/2023 03:10:18 pm
Although I meant to do this months ago, thank you to all you contributed to this discussion. It was very helpful in helping us come to a solution regarding materials on this project.
Reply