We have a production facility with a roof height of 55-ft. Someone has decided that storage sprinklers would be more appropriate.
How far from the roof would it be acceptable to install K11.2 (K160) spray sprinklers? Is this approach even acceptable? Does the extreme height of the roof affect the best sprinkler height? I vaguely remember Russ Fleming did a paper on the hottest point in the fire plume being some 10 % (?) of the ceiling height from the roof. Must have been 20 years ago or more. Hopefully someone can help me with information or views on this subject on an appropriate height from the roof. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
9 Comments
JI
6/15/2023 08:08:16 am
NFPA is rather silent on this issue unless storage is mentioned. FM guidelines has different requirements for ceiling heights as they get higher within DS 3-26.
Reply
FM has their own guidelines on everything. It seems as if they are close to something I read a long, long time ago. 'They seem to be able to swallow a camel, but gag on a gnat.' Pretty much sums up all politicians as well. Just my 2 cents worth. (That and $5.00 will get you a cup of 25 cent coffee.)
Reply
moises OLMEDA
6/15/2023 08:25:11 am
I think your guess is reasonable, even though the hazard category is between OH & EH, a bigger droplets have a better chance to control de fire and avoid the heat and turn into steam.
Reply
Jesse
6/15/2023 08:38:12 am
Seems like you have a few questions. First, make sure that whatever sprinkler you use is listed for the hazard class. Most storage sprinklers carry listings for OH.
Reply
Todd E Wyatt
6/15/2023 08:38:15 am
2022 NFPA 13 includes the following references to “distance below ceilings” :
Reply
Todd E Wyatt
6/15/2023 08:38:47 am
2022 NFPA 13 Chapter 20 General Requirements for Storage states the following :
Reply
Todd E Wyatt
6/15/2023 08:39:53 am
FAQ
Dan Wilder
6/15/2023 08:42:35 am
If the question is to lower sprinklers below the standard NFPA written or Sprinkler listed deflector distances below the roof deck, no, there is no provision within NFPA for that.
Reply
Pete H
6/15/2023 02:54:18 pm
55 foot building using storage heads?
Reply