Is there any reason in code (NFPA 13 or 20) that you cannot tie a Fire Department Connection (FDC) line to a pump bypass line as long as the FDC line is downstream of all control valves on the pump bypass?
Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
6 Comments
Alex
10/8/2021 05:38:24 am
Hi Anonymous,
Reply
Anthony
10/8/2021 08:10:27 am
By definition, if you tie in past your pump control valve and after the bypass check, you're on the system side of the pump.
Reply
Glenn Berger
10/8/2021 08:17:43 am
Does your building have a single sprinkler riser or multiple risers? Or multiple standpipes and sprinkler risers?
Reply
sean
10/8/2021 08:49:41 am
no issue
Reply
Jesse
10/8/2021 09:00:47 am
No issue at all and done quite frequently. As long as it connects downstream of bypass check valve.
Reply
CJ Bonczyk
10/8/2021 10:19:49 am
Yes you can as long as it downstream of the check valve along the bypass assembly.
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop June '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
July 2024
PE PREP SERIES |