Are you allowed to have a valve off the standpipe feeding a hose valve that is not in the stairwell?
Working in a high rise building with two stairwells. It is dual fed with combination riser standpipes. On the tenant space there is a hose valve and they want a butterfly on the feed for the hose valve, always thought that was not allowed but couldn’t find it. Thanks in advance. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
7 Comments
Dan Wilder
8/8/2023 07:49:16 am
Yes, allowed and it's required when the single hose valve is greater than 40' along a branch line (14-22' - 6.3.3). Minimum sizing & hydraulics per 14-22' 7.8 & 7.10
Reply
Glenn Berger
8/8/2023 08:05:02 am
Yes, you can valve off a hose valve. Reminder to install a tamper switch on this valve.
Reply
Jesse
8/8/2023 08:56:55 am
Yep. The valve will need to be supervised though.
Reply
Todd E Wyatt
8/9/2023 08:18:40 am
SUMMARY
Reply
Todd E Wyatt
8/9/2023 08:19:05 am
REFERENCES
Reply
Todd E Wyatt
8/9/2023 08:20:21 am
REFERENCES continued ...
Reply
Alex
8/10/2023 07:34:52 am
Yes, this is allowed contingent the valve is supervised.
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop June '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
July 2024
PE PREP SERIES |