Are air compressors for dry fire sprinkler systems required to be listed?
Thanks in advance. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
3 Comments
Dan Wilder
4/5/2024 07:23:02 am
Depends on the year of NFPA 13 referenced. In all cases, plant air/nitrogen is still a viable source and not required to be listed. Other NFPA's (like 14) are a little behind but will correlate with 13 eventually.
Reply
Franck
4/5/2024 09:06:40 am
No, as you can supply air or nitrogen from the plant process equipment.
Reply
Anthony
4/10/2024 07:33:17 am
This.
Reply