Suppose on-site water storage for firefighting is required, and an existing tank is on-site sized for the existing building.
Can I add a second tank on site (not connected to the first tank) and just size it for the additional water required for the second building? Ex. A larger building requires a 10,000-gallon tank, while a smaller building requires a 5,000-gallon tank. Can I just install one new 5,000-gallon tank (10,000-5,000 = 5,000 gallons)? Or would the tanks need to be connected so there is no shortage of water? Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
5 Comments
M. Newell
7/17/2024 08:10:18 am
Normally your tank is sized for the largest demand on site.
Reply
Dan Wilder
7/17/2024 08:24:37 am
The tanks need to be connected so that there is one continuous, uninterruptable water supply sized for the largest demand....there would be no nice way to pull water from one tank then the other without possibly cavitating the pump.
Reply
Jack G
7/17/2024 11:34:05 am
NFPA 1 indicates the fire flow need not be added to the sprinkler demand, however, the AHJ, and pjt Engineer may have a different opinion and that is what you may have to follow.
Reply
Glenn Berger
7/17/2024 01:08:47 pm
Since the comment states that the storage tanks are 5,000 gallons and 10,000 gallons in size. Tanks that are this small do not include supplemental fire fighting hose streams. And most definitely not for any realistic suppression system discharge time.
Reply
Jesse
7/18/2024 07:57:39 am
No, because it needs to be a continuous and uninterruptable fire water supply. Now granted, we're talking really small tanks. For example, I have a current project with 180K gallon storage.
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop June '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
July 2024
PE PREP SERIES |