Where does - or does - NFPA 13 and NFPA 13D (2022 Edition) say that hydraulic calculations should be run from the most remote sprinkler to the water supply?
Apparently some hydraulic calculation programs print out the results backwards, which makes them harder to follow. Thanks in advance. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
12 Comments
Dan Wilder
3/2/2023 07:23:46 am
There is no requirement for direction of calculation that I can find in the Chapter 28.4 section. Just that the node tags need to be there along with several other characteristics/identifiers like elevations for each, distance between, fittings & eq lengths....
Reply
Glenn Berger
3/2/2023 08:21:55 am
The requirement is that the most remote area be calculated. The how program displays the remote area is not a requirement.
Reply
Nate
3/2/2023 08:23:29 am
I am actually attending EKU currently, and one of my current class is sprinkler design, But in NFPA 13, 2022 chapter 19 basically answers your question in a code way. But a short answer in class we are currently just talking about your basic wet steel pipe system, there is a calculation to find your design area - (area of room (ft^2) / sprinkler coverage area (ft^2)) which is the furthest from the supply. Note: I am a rookie with sprinkler design and still learning
Reply
Chris
3/2/2023 08:32:36 am
Nate, your answer is correct for hand calculations! These are CRITICAL for your understanding of how to read calculations produced by programs, and then find the blockages to fix to optimize the pipe sizing. Keep learning and know that this industry is secretly very hard, very unique, and very rewarding!
Reply
James Evans
3/2/2023 09:00:35 am
An interesting thing about calculations. The program does not care about direction of the calculation, in the long run, the program looks at a system like a long straight pipe with flowing outlets at the end. there are no elbows or tees, those are input as equivalent lengths of straight pipe. so the computer sees only a very long run of straight pipe with a quantity of water flowing through it and outlets at the end in a straight line and each outlet relieving the flow until it his zero water left in the pipe.
Jesse
3/2/2023 08:25:13 am
I'm not familiar with anything requiring a directional calc. The nature of the Hazen-Williams calc would pretty much allow it to be reversed.
Reply
Alex
3/2/2023 08:36:39 am
I am not aware of any requirement. I was taught that as long as the nodes on the drawing match the calculation sheet and that the two can be reviewed as one, the nodes can be “dog” or “cat” for that matter.
Reply
Anthony
3/2/2023 08:42:36 am
You have to run the calculation from the most demanding head to the supply for a demand calculation. Thats just how a DEMAND calc works. It determines the bare minimum supply condition required to operate the system. You can arrange the nodes in the calculation in any logical manner you'd like. NFPA 13- 16 does detail out the method for arranging calculation data on a detailed work sheet in chapter 23.3. and the procedure to follow is in 23.4 Also in the annex (specifically A23.3.2(c) there is a light smattering of examples.
Reply
Chris
3/2/2023 08:43:18 am
As mentioned above, NFPA 13 22 - 28.2.4.7.5 states that "Calculations shall begin at the hydraulically most remote sprinkler". This comment is likely geared towards hand-calcs, and ideally should possibly be rephrased? In my career, only 1 of the hardest engineers in my region has ever commented on my calcs they didn't technically start at the most remote head. I then reorganized the way my calcs are entered to fix this.
Reply
Franck
3/2/2023 09:46:28 am
Chris indicated the right reference for the most remote sprinkler to start the hydraulic calculation.
Reply
James Art, FPE
4/4/2023 11:47:28 am
Much easier to review calcs if if proper order.
Reply
James Art
4/4/2023 12:06:57 pm
Oops. Just forgot to ask the site to notify me for responses.