Hi All, Is there a code reference on the maximum amount of time allowed to close a wall PIV (or any valve for that matter)?
I have a Wall PIV that is hard and slow to turn, and takes about 30 minutes of fighting to fully close. Servicing of accessible components has not helped. I probably won't be able to get funds to repair/replace unless I can quote a code violation. I have only found a minimum amount of time, but nothing for a maximum. Thanks in advance! Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
11 Comments
Dan Wilder
11/17/2022 07:53:35 am
Nothing I am aware of. Minimum is 5 seconds, that I know.
Reply
Adam
11/17/2022 08:10:46 am
If this valve needs to be closed in an emergency, 30 minutes of uncontrolled flow can cause a lot of water damage, and disrupt operations/productivity for an indefinite period of time. Perhaps a replacement could be justified on this basis?
Reply
Franck
11/17/2022 08:14:34 am
The minimum is to avoid a waterhammer effect if closing too quick.
Reply
Glenn Berger
11/17/2022 08:15:45 am
You might be able to use NFPA 25 Chapter 13 as a valve that has been damaged. Any time of coercion or supplemental lubricant requirement are proof of a damaged valve. But as for a hard and fast rule about timing, I am not aware of one.
Reply
Matt Couto
11/17/2022 08:19:10 am
I think you might be coming at this from the wrong angle. The minimum time requirement (to my knowledge) is to prevent water hammer.
Reply
Jesse
11/17/2022 08:27:51 am
Clearly the valve is damaged. While you may not find a coed reference, having the purse holders consider 30 minutes of uncontrolled water flowing inside the facility as someone wrestles the valve.
Reply
Evan Lesh
11/17/2022 08:46:29 am
This should definitely be repaired or replaced for many reasons.
Reply
OP
11/17/2022 02:37:19 pm
Thanks, as "unreasonable force" is necessary to operate the valve, I can reference this code as need for repair.
Reply
Eric R
11/17/2022 10:00:21 am
Since it's clear we all agree that this is unacceptable, here are some of my thoughts on how a contractor should handle this kind of situation to protect their liability.
Reply
Ronnie Morales
11/18/2022 07:35:46 am
NFPA 13, 2022
Reply
Panos
11/19/2022 12:24:11 pm
This is a crooked valve, get it repaired or replaced.
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop June '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
July 2024
PE PREP SERIES |