Our State Department of Natural Resources requires a double check on all water based sprinkler systems and an RPZ backflow when additives such as foam or antifreeze are used.
The rule is for containment. Meaning that the first available connection requires the backflow preventer. With the details shown in NFPA 13 there are examples of check valves with a drilled clapper as well as an appropriate backflow preventer in the examples shown appear to be isolation devices. NFPA 13 FIGURE 8.6.3.3 shows a backflow preventer and includes an expansion tank. If the entire building is protected by an RPZ the water department is satisfied. When approaching the antifreeze pipe arrangement FIGURE 8.6.3.3 wouldn’t a swing check without a drilled hole be equal to the backflow preventer? Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
8 Comments
Mike
10/19/2023 08:09:23 am
I wouldn't say "equal" so much as "acceptable in lieu of". The check valve and drop loop minimizes but doesn't eliminate the possibility of dilution. NFPA doesn't mandate which arrangement you must pick. You really are weighing the cost to replace the premixed AF solution if it becomes too dilute vs the cost of an RPZ, expansion tank and forward flow testing the RPZ in the future. Premix AF is rather expensive, but so are RPZs and forward flow tests etc.
Reply
Dan Wilder
10/19/2023 08:28:22 am
No, a check valve does not perform the same as a backflow assembly. Even two check valves in line with each other do not perform the same.
Reply
SCHULMAN
10/19/2023 09:36:20 am
Dan's answer .... No, not the same.
Reply
Anthony
10/19/2023 10:32:30 am
No. The purpose of a backflow device (BFD) is to prevent cross contamination with the water supply and check valves, even in series, does not do that. PRV's would work best of you are concerned about expansion issues but keep in mind a RPZ is still required for any hazardous system, not just foam or antifreeze.
Reply
Glenn Berger
10/19/2023 12:38:52 pm
A check valve is not a substitute for an approved backflow preventor.
Reply
RYAN HINSON
10/19/2023 01:04:18 pm
The location for the BFP required by your AHJ is indeed referencing the lead-in to your building and not at your antifreeze extension location. A backflow is already going to be required upstream of any non-potable system connection to a potable water supply per the applicable plumbing code for the jurisdiction (See IPC 2012 Section 608.16.4)...including any water-based sprinkler system.
Reply
Jesse
10/20/2023 08:21:22 am
No, not really. These aren't the same device
Reply
Mark
5/2/2024 10:12:41 pm
If you have an RP at the Anti-Freeze loop, are you required to have one at your riser as well? Or can you be ok with having a DC at the riser??
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop June '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
July 2024
PE PREP SERIES |