This week's breakout is a summary of fire protection requirements for elevators under the International Building Code, NFPA 13, and ASME A17.1. While there are some staples across all elevator types, there's also a number of exceptions and opportunities for flexible design approach, depending upon which edition of NFPA 13 and 72 are applicable. Sprinkler Elevator Requirements
Sprinkler at the Top of Shaft Provide when:
Sprinkler near the Bottom of Shaft (Pit) Provide when:
Want to see more like this? Subscribe to our Blog.
Confused
6/6/2019 10:40:25 am
If IFC or IBC do not require the building to be sprinklered (and by extension NFPA 13 is not required), would this still apply? Is machine room and shaft protection required simply because an elevator is installed?
Joe Meyer
6/6/2019 10:46:16 am
Typically no, if a building does not have a sprinkler system then there is no requirement for a sprinkler within the shaft. Good question though.
Confused
6/6/2019 10:55:42 am
I have heard that quantity of hydraulic oil can require sprinklers. Assuming it's class IIIB liquid, Hazardous use group isn't triggered until over 13,200 gallons of use or storage. Typical tank and system volume is a lot lower.
Evan Verduin
7/11/2019 05:35:55 am
I have a VB building that is 2 stories and under size/use requirements that would trigger sprinklers. Thus, no sprinklers per IBC Chap. 9. The shaft is not rated as well, per IBC chapter 7, only connecting two floors. The elevator is hydraulic type. I’m under the impression NFPA 13 would not apply here since the IBC is not requiring sprinklers, any assistance or precedents? Help would be great!!!
Joe Meyer
7/15/2019 01:29:03 pm
Evan,
I've seen a lot of buildings with sprinklers in the elevator shaft which seems may be over an above the requirements of NFPA 13. I suspect one factor is there is very little cost installing a sprinkler during construction, but enormous cost to adding a sprinkler to an elevator shaft of a finished building and contractors don't want to take the chance that some AHJ will tell them to put them in later.
Mike Jones
7/30/2020 11:25:11 am
How do you sprinkle a elevator pit if the elevator is outside In States where the temperature drops blow freezing?
Jonathan Sullivan
7/30/2020 11:58:51 am
Mike - hopefully you've addressed in your code analysis that you do in fact need one for this elevator. You probably have a few options: condition the shaft (lots of energy code/aesthetic/structural issues with this), use a listed heat trace/wet system, use a listed antifreeze, or install a dry system with a heated valve room or valve enclosure. Comments are closed.
|
ALL-ACCESSSUBSCRIBEGet Free Articles via Email:
+ Get calculators, tools, resources and articles
+ Get our PDF Flowchart for Canopy & Overhang Requirements instantly + No spam
+ Unsubscribe anytime AUTHORJoe Meyer, PE, is a Fire Protection Engineer out of St. Louis, Missouri who writes & develops resources for Fire Protection Professionals. See bio here: About FILTERS
All
ARCHIVES
May 2024
|