One of the most common and basic issues many of us encounter in fire sprinkler design or during on-site review is whether a sprinkler is considered to be obstructed. While the premise of the obstruction tables within NFPA 13 is fairly straightforward, there are a handful of variations in the tables that are dependent upon the edition of 13 being used, the sprinkler type, and in some cases the orientation of the sprinkler.
This reference tool below was built to quickly determine whether a ceiling-mounted element is considered an obstruction. It can be especially helpful during sprinkler layout or during site review where lugging the entire code volume might not be practical
Common examples of where obstructions are considered are with sprinklers adjacent to surface-mounted lights, soffits (not against a wall), mechanical equipment in walk-in coolers and freezers, signage, banners, lowered ceilings, thresholds above large openings, raised ceiling pockets, or exit lighting.
Give this a try and let us know what you think in the comment section below (the red highlighted cells are input values). Having trouble viewing? Click here to see the full tool.
jose bohorquez
7/15/2017 08:02:52 am
Como la puedo descargar
Jeremy Ewan
7/17/2017 09:17:31 pm
Always wanted to graph these tables but never thought about it long enough to figure it out and actually do it.
Matt Ruhrer
7/18/2017 07:31:19 am
Great tool, this should be in an app for AHJ's and others for an easy reference.
Daniel Garcia
10/9/2017 02:14:03 pm
Sorry, I'm a little bit late reading this (just heard about this website). I tried to download the spreadsheet but it didn't work. Can you e-mail it to me?
Basil
11/15/2017 01:38:38 am
The spreadsheet appears not to be available for download anymore. Kindly e-mail it to me.
RDT8880
1/3/2018 11:28:42 am
The articles, graphics, and tools presented are valuable and much appreciated. Excellent learning tools and helpful to all. Thank you!!!
Smith Choi
1/14/2020 10:10:38 am
Can you email me the spreadsheet for basic tool for ceiling obstruction. Thanks.
Joe Meyer
1/14/2020 10:12:24 am
Hi Smith! These are available as a complete software toolkit package - see here: https://www.meyerfire.com/toolkit.html Comments are closed.
|
ALL-ACCESSSUBSCRIBEGet Free Articles via Email:
+ Get calculators, tools, resources and articles
+ Get our PDF Flowchart for Canopy & Overhang Requirements instantly + No spam
+ Unsubscribe anytime AUTHORJoe Meyer, PE, is a Fire Protection Engineer out of St. Louis, Missouri who writes & develops resources for Fire Protection Professionals. See bio here: About FILTERS
All
ARCHIVES
July 2024
|