Last week I discussed across a common misconception with porte-cochere sprinkler requirements and how code addresses sprinkler protection for these structures. This week I’m diving a little deeper with some estimates of how a porte-cochere fire would actually affect a main building, based on distance from the building. It’s important to note that this exercise is largely academic: with the calculations below I’m making some gross assumptions that overly simplify the situation. This has not been vetted with Ph.D. experts nor gone through full scale fire testing. I’m just running some basic numbers with big assumptions to illustrate a point. Heat Transfer From what science gives us - heat is transferred by three methods. Conduction, convection, and radiation. Conduction is the transfer of heat by objects touching each other. The direction of transfer is dictated by hot-to-cooler materials in direct contact. Convection is the transfer of heat caused by the movement of gas (or a fluid). The direction of transfer is largely dictated by overall movement of the fluid, and for smoke tends to be vertical. Radiation is the transfer of heat from the emission of electromagnetic waves. The direction of transfer is in all directions, but can reflect and re-emit from other surfaces. Heat Transfer for a Flame For a flame, depending on the fuel, most of the heat will be transferred away from the flame source primarily by convection. The chemical reaction (oxidation) of a flame will cause gases to heat. The heated gas’ molecules will become more active and less dense. With less-dense gas than surrounding cooler air, the warm gas will rise up and away from the flame source and carry solid particles forming hot smoke. Radiation will typically comprise 20-35% of the overall heat release rate for a fire. Radiation transfers heat from the source in all available directions until it contacts another surface. Once in contact with other surfaces, radiation can be absorbed or re-emitted from the surface, depending on the surface material. Conduction is the least important mode of heat transfer in an open fire. Radiation near a flame’s origin, for example, often emits and heats up adjacent surfaces with more impact than conduction. For wall assemblies, conduction of heat through penetrations becomes important, but for flames in open environments conduction plays only a small role. Three Porte Cochere Scenarios 100-foot Separation Now imagine a porte-cochere that is 100 feet (30 m) from the face of a larger main building to the center of the porte-cochere. If the porte-cochere is completely inflamed, how would it transfer heat to the main building? It would transfer heat only by radiation; and in very small amounts. Assumptions include a 5 megawatt (MW) fire from a wood-built porte-cochere, a 100-foot (30 m) center distance from the main building, an atmospheric transmissivity of 0.95, and a 30% of the overall heat loss as radiation. Using the Lawson and Quintiere Point-Source Method, the incident radiant flux (a measure of the heat energy per area) is 0.13 kW/sqm. This radiant flux is about 10% of the flux for a 1st degree burn on unprotected skin. 30-foot Separation Now move the porte-cochere to be 30 feet from the face of the building. Radiation will again transfer heat to the face of the building, but in a much larger amount. Because radiant flux is related to the inverse square of the distance between the targets, this 30-foot distance will actually have a radiant heat flux 10 times greater than a porte-cochere fire 100 feet away. For the same size fire as before but at 30-feet, this could be about enough heat for a 1st degree burn. At the 30-foot distance, however, heat transfer to the main building is still primarily by radiation. The hot, buoyant smoke is still primarily driven upward from the porte-cochere and would likely not reach the main building unless strong winds directed the hot gases. 10-foot Separation Now imagine this same porte-cochere, but this time centered only 10 feet (3 m) from the main building. Radiation heat transfer is now 10 times greater than the 30-foot distance, and 100 times greater than the 100-foot distance. At only 10 feet from a 5 MW fire, the heat flux is enough easily cause 2nd degree burns for unprotected skin. Additionally, this heat flux is now approaching the critical heat flux for ignition of some building materials. The critical heat flux is the minimum amount of heat, per area, required to cause ignition. There's several factors that contribute to ignition including exposure time, material thermal properties, surface temperatures, and the actual heat flux versus critical heat flux - but for our purposes I'm only showing this critical heat flux for a couple siding materials. Wood, for instance, has been tested to have a critical heat flux of approximately 10 kW/sqm. Vinyl siding has a critical heat flux of approximately 15 kW/sqm (both values from SFPE Handbook of Fire Protection Engineering, Table A.35, 5th Volume). When we look at the heat flux already produced by a fire of this size at 10 feet we can see that we're already approaching the critical heat flux for both wood and vinyl. Actual Separation
Now let's speak in practicality. Porte-cocheres are built to allow visitors to enter and leave cars without exposure to rain or sun. Is a 30-foot or 100-foot separated porte-cochere provide any value to a building? No, of course not. This exercise just shows that with reasonable assumptions, a 10-foot physical separation assuming a 5 MW fire begins to approach the critical flux needed to ignite a nearby building. Fire Size Would the actual fire be 5 MW? It's difficult to predict and will vary widely by the materials used and the shape it conforms. A point-source approximation is a large oversimplification given that a wooden canopy would burn in a very different configuration than a condensed pile of wood pallets, for instance. Convection What about convection? Up to now we've still only discussed heat transfer by radiation. If a porte-cochere is close enough to a building, convective heat transfer from the hot smoke will begin to contact the main building and heat surfaces along the face of the main building. This could also be aided by wind conditions as well. As I explored a little last week, a porte-cochere that is only separated inches or a couple feet from a building is hardly any different than a porte-cochere that's attached to the building. That's largely because of convective and radiative heat transfer. The further away the porte-cochere is, the less convective heat transfer plays a role and the lower amount of radiative heat will be transferred. Fire-Resistive Construction What if we create a firewall or fire barrier? Both would slow the spread of fire and help prevent the main building from burning. The International Building Code relaxes the physical separation with fire-resistive construction, and for good reason. Heat flux becomes much less important when the exterior is of non-combustible construction. Summary It can be easy to get lost in code minutiae and live by the black and white lines of what code reads. I find that it's important to remind myself about context about each building and where good engineering judgement plays a role in protecting buildings from fire. This overly-simplified series of calculations just shows the tiers of radiative heat transfer and how much it is affected by the separation distance. The further away a building is from another, the less convective heat transfer plays a role (if any) and the less radiative heat transfer occurs. If you found this interesting, let me know by leaving a comment here. Always happy to hear other opinions. If you don't already follow the weekly blog, consider subscribing here. Thanks for reading!
In February of last year I put together a flowchart that covered sprinkler requirements for exterior projections. If I had a Top-10 Articles list, it'd be on it.
If you haven’t read it,here’s a link to the original article. Porte-Cochere Updates Since I wrote this article and posted the original flowchart, I’ve received some encouraging feedback and thoughtful comments. I’ve updated the flow chart this week to address specifically sprinkler protection of porte-cocheres: What's a Porte-Cochere? First, because I have no idea where the term “porte-cochere” originated, I’m talking about the covered entrance where vehicles can pass through as part of an entranceway to a building. Not to point fingers, but I’m guessing the term “porte-cochere” was dreamed up by an architect to disguise the fact that they’re sticking a carport on the front of their building. Maybe it’s my Missouri roots, but what we’re talking about here are just fancy carports that can be driven through. Now stepping down from the soapbox… "If It's Not Touching the Building..." Stop me if you've heard this one before. One common assumption I’ve heard repeatedly from architects and contractors concerning porte-cocheres is that sprinkler protection isn’t required for porte-cocheres if they are not connected to the main building. Unfortunately, that's not justified by code. It is true that porte-cocheres, on their own, often do not require fire sprinkler protection. They will generally fall under a Type U (Utility and Miscellaneous Group) Occupancy, which do not require fire sprinklers by IBC 903.2. However, in order to qualify as a separate “building”, the International Building Code requires a physical space separation, a fire-rated separation, or a combination of both. In terms of a porte-cochere attached to a main building, the porte-cochere would be considered a separate building by any one of the following:
As an example, if the main building is a Type V-B (combustible construction), Residential R-2 Occupancy (such as a Senior Living facility with more than 16 people), then the minimum requirements for a porte-cochere as a separate building would be:
Applying Logic From a practical standpoint, what is the difference between a porte-cochere that’s six inches from the main building and one that is touching the main building? None. Zero difference. I’ll explore this from a scientific perspective in next week’s article, but in short - conduction heat transfer makes little difference in the spread of fire from one structure to another. Want to know why forest fires can “jump” across highways? It’s not because trees are locking branches above roadways – it’s because of radiative heat transfer. So why do we get so tied to the concept that if the porte-cochere isn’t touching the main building that it’s as if it doesn’t exit? I’m not sure exactly, but it seems to come up quite frequently. One Note on Concealed Spaces NFPA 13 has two separate sections that affect porte-cocheres. The first is protection below overhangs, canopies, & porte-cocheres. This article and the flowchart address this situation. The second section is protection within concealed spaces. If your porte-cochere does not require sprinkler protection per the building code, then no sprinklers are required regardless. If that's not the case, and your porte-cochere has concealed spaces within it, check out NFPA 13's Special Situations section to see if the concealed spaces require sprinkler protection. These may still be required to be protected even when sprinklers can be omitted below the ceiling. This show ups in Section 8.14.1 of the 2002 Edition, Section 8.15.1 in the 2007-2016 Editions, and Section 9.3.18 in the 2019 Edition. Losing the Forest for the Trees I sometimes find that when assessing code it is easy to lose the forest for the trees. Sometimes I can be so fixated on finding one specific answer that it is easy to step back and assess the ‘big picture’. Addressing overhangs and canopies can get that way. While I don’t always get the opportunity to address fire protection intent with a building owner, I have to keep in mind that code only prescribes the minimum requirements. We can always elect to improve fire protection & life safety above code minimum. Two recent local fires come to mind when looking at how sprinkler protection affects overhangs and how different owners were impacted very differently. The first fire occurred at an apartment complex when a tenant left a lit cigarette on the third story balcony of an apartment complex. The cigarette started a fire on the unprotected balcony, which spread into the apartment attic (without draftstops) and quickly spread across the attic of the entire building. The upper two levels were badly damaged along with the entire attic and roof needing replacement. Another fire occurred, more recently, at a three-story office with a porte-cochere. A car fire underneath the porte-cochere activated a single sprinkler which suppressed growth until the fire department arrived. The porte-cochere had smoke damage, but the fire had no impact to the main building. No downtime, no multi-million dollar rebuild. From the photos it was difficult to see any impact from just inside the main entrance. These are two different situations of course; the first likely an NFPA 13R and the second an NFPA 13 system. Nonetheless it raises the issue of making sure that we, as professionals, inform and have dialogue with the building owner to not just determine what code minimums require, but what levels of protection may serve them best. This Month's Sponsor I'd like to introduce this month's MeyerFire sponsor with Engineered Corrosion Solutions. They are experts in the corrosion space for fire sprinkler systems and have a long list of helpful resources on their website. As a side note, some of their original whitepapers and case studies were instrumental for me in my understanding of current corrosion challenges. When should we specify galvanized pipe? Is MIC or oxygen-induced corrosion a bigger concern? What can we do to stop corrosion entirely? They have it all here. Thanks to the ECS team for helping promote this site and supporting my efforts to develop new resources for the industry. Next Week Next week I'll explore the concept of porte-cochere separation distance, but from a modeling perspective. How much does the distance impact radiative heat transfer? How does convective heat transfer play a role? I'll explore this in more detail and from a calculated perspective next week. If you don’t already get these weekly articles via email, subscribe here. If you know someone who might be interested, please pass a link along. Thanks and have a great week! Sometimes the best inspiration for new tools on this site come from basic frustrations with repeated tasks. The past few weeks I’ve finally come to the point where I needed to scratch an itch – plumbing fixture counts. What does this have to do for code & life safety? It doesn’t – other than (generally speaking) code summaries will often address plumbing fixture count minimums as part of the overall building code evaluation. Here’s my scratched itch – a calculator that will populate minimum requirements for plumbing fixture counts based on the 2018 International Building Code & 2018 International Plumbing Code. Now, with only four inputs you can quickly grab the minimum fixture counts from the 2018 IBC. It’s more than likely that something already exists in the vast spans of the internet for this, but in the meantime at least I know we all can stop wringing the calculator for a few basic number crunches. If you’re already a Toolkit user, you can download this update and use it right away on the downloads page here: www.meyerfire.com/downloads If you’re not already a Toolkit user, why not? Join in on all the expanded tools we have by getting the Toolkit here. Is this something you’d use? If you’d find this useful and would like to see it expanded to other editions of the IBC (or other standards), let me know by commenting here. I’d be happy to break this out for prior IBC editions if it’s something that’d be beneficial. There’s no real way around it: I love cheatsheets. In a design course in college we received 5x7 index cards to include any handwritten notes we wanted for an upcoming final. I wrote so much on that card with handwriting that was effectively size-4 font that it could have been displayed as a work of art. Nearly an entire semester summarized to a 5x7 card. It was a thing of beauty. While I no longer have a need to write so small, I still enjoy having information organized so that it is extremely easy to access. If you haven’t seen these before, here are a couple cheatsheets I’ve created so far: Summary of Differences of NFPA 13, 13R, and 13D Sprinklers & Passive Fire Protection Options
Last week I covered important considerations surrounding fire department connections from a design perspective, which was a joint-effort with QRFS covering the topic. At some point I’ll compile the best blog posts and resources into a hardcover reference book. For this week, however, here’s a cheatsheet on requirements surrounding fire department connections across NFPA 13R, NFPA 13, and NFPA 14:
I'm very excited to announce that starting this September we will have a monthly site sponsor.
As you may know, MeyerFire.com was created to help you do great things in fire protection. This site was built to promote the practice and empower professionals in the fire protection community. How? By creating highly-visual, high-quality content and resources to support and connect the people who do fire protection the best. You. Each month we'll showcase an exclusive sponsor that supports our efforts at MeyerFire. The only difference you might notice is a new a sidebar image to the right on the site and a horizontal banner towards the bottom of emails. I'm very encouraged that the sponsorships will allow me to invest more time and development in content and resources that ultimately will help you continue to do great things. Sound like a stretch? Don't take my word for it. I hope you'll see for yourself later this year what the support of the sponsorships will bring to the site. In the meantime, please consider supporting our sponsors by clicking on the images and checking out their content starting this September. If you're interested in sponsoring the site with your campaign, don't hesitate to contact Joe directly at [email protected] for more information. Thanks for all of your continued interest and support! Why are fire department connections (FDCs) so important to a suppression system? They are the link between initial response and supplemental help. Despite appearances, sprinkler systems are not intended to discharge forever. Their goal is to suppress long-enough that firefighters can take over and finish the job. Standpipe systems exist to extend the reach of the fire department in tall, wide or complex buildings. Manual standpipes depend upon pressure and flow from the fire department. What single piece of equipment is relied upon to make the transfer? The FDC. This week's article is an overview of fire department connections from an engineer’s perspective. It is one part of a two-part series covering fire department connections. Read more from a supplier’s perspective at Quick Response Fire Supply here. Authority Intervention Needed Fire department connections are a unique piece of a suppression system in that they’re not just governed by the designer and code. NFPA 13 and 14 require that fire department connection type and location is coordinated with the Authority Having Jurisdiction. Early in design, prior to bid, I’ll call the local fire marshal and coordinate each of the following big-picture elements: Coordination Item 1: Type of Fire Department Connection The most popular types of FDCs? Siamese (2 x 2-1/2" threaded connection) and Storz (4" or 5" with or without 30-degree elbow). In my very unscientific study of jurisdictions I call (nearly half are local to my area), I've found the following; 73% use Siamese-type 2-1/2” fire department connections, 11% use 4” Storz connections, and the remaining 16% use 5” Storz connections. Of these, 13% have special requirements such as Knox Locking caps, 30-degree elbows, or irregular threading. There’s no right or wrong answer here – I just want to be sure what I’m calling for or showing on plans match what the jurisdiction uses. Large diameter Storz-type fire department connections have become more common for their ability to quick-connect a single hose and flow large amounts of water. Coordination Item 2: Location of Fire Department Connection The most obvious coordination during design is the location of the fire department connection. My design preference, driven by installation effort and cost, is typically in the following order: 1. Wall-mounted FDC, adjacent to the sprinkler riser 2. Wall-mounted FDC, remote from the riser (such as the front of the building) 3. Freestanding FDC, downstream of a site backflow pit or hotbox 4. Freestanding FDC, connected underground into the sprinkler riser room The first couple options are not always workable and depend on the building. Sometimes the water supply and riser room are in the back of a building inaccessible to the fire department. This would be a bad place for an FDC. Sometimes the front face of a building is "grand view" with large glazed curtain walls and no room to mount a fire department connection. This comes up with large offices or modern schools. Sometimes a building-mounted FDC doesn’t make sense with major hazards; why risk firefighter safety in these cases? High-rises, for instance, require multiple FDCs due to the potential for falling glass that could injure firefighters or sever hoses. If there's potential for wall-collapse (think high-hazard warehouse wall) then a wall-mounted FDC also may not make sense. Freestanding FDCs can make a lot of sense for projects like these. Considering most of my work is two stories or less and light commercial, it may not be surprising that roughly 85% of projects include building-mounted FDCs. The remaining 15% have necessitated freestanding FDCs. Some jurisdictions require freestanding fire department connections, but it typically depends on the type of building and hazard presented. Coordination Item 3: Distance of FDC to Nearest Hydrant As a designer it would be great if I could operate in the dark. Send me all the information I need to do a design, I do it, and everyone’s happy. If it were that simple, though, we’d probably already have machines design and do it without downing two bags of Doritos and a half hour of facebook each day. Back to the topic: FDC-to-hydrant distance has an impact on the tactical approach in firefighting. Many designers & installers in our field are current or former firefighters. They could readily speak to this. I’m not one of them, but I can imagine that having to shut down a major roadway or cross a parking lot with hundreds of feet of hose quickly during an emergency is not exactly the easiest thing to accomplish. As a result I like to ask AHJs what distance the FDC should be to the nearest hydrant. Of my highly unscientific and locally-biases results, 41% of jurisdictions require a hydrant to be within 100 feet of the FDC or less, 47% require a hydrant to be within 150 feet, and only 16% of jurisdictions require a hydrant within 200 feet or more of the FDC. These three elements are a part of my code calls. Next week I'll distribute my FDC Cheatsheet that outlines requirements for FDCs across NFPA 13, 13R and NFPA 14. If you haven't already subscribed, consider doing so here. What do you look to coordinate with the AHJ? Discuss your experience here. Want more coverage on fire department connections? See the other half of our two-part series on fire department connections here: Quick Response Fire Supply. Since the entirety of fire sprinklers systems normally depend on heat to actuate a sprinkler – it is an important topic. Before I ever started in shop drawing design. I prepared bid packages that specified important aspects of system design. One of the luxuries of living on the front-end (some say "theoretical") side of design was delegating the sprinkler temperature selection. Selecting appropriate sprinkler temperatures is not difficult. That said, making an egregious error with a temperature too low could cause an inadvertent discharge. Considering how much damage this could do, there’s quite a bit of liability there. Temperature is one of the three concepts I look to address when designing sprinkler systems in commercial kitchens. Consideration #1: Heat In high school I worked a few years in a kitchen. I hated it. It was stressful, always hot, and the cook line seemed to play the same six songs on repeat. Even now when I hear The Hand that Feeds by Nine Inch Nails, my palms start to sweat. I get thrown back to that smoky, steamy kitchen and getting yelled at for bringing out entrees while the salad course wasn’t finished. Despite it being in a country club, it was awful. Maybe I’m sensitive (if not dramatic), but when I design sprinkler systems for kitchens I’m acutely aware of how hot those spaces can be. We want sprinklers to operate early enough in a fire when they can be effective. We also don’t want unintentional activation with a temperature too low. NFPA 13 directs sprinklers to be ordinary or intermediate temperature unless specific heat-producing sources or hazards exist. For commercial cooking equipment, if a sprinkler could experience ceiling temperatures over 100 degrees F (38 C), then they must at least be intermediate temperature (NFPA 13 2002-16 8.3.2.2, 2019 9.4.2.2). I’ve never measured temperatures on the cookline but I would suspect this would be easy to achieve. NFPA 13 also directs temperature selection to be based on nearby heat sources (in 8.3.2.5 2002-16, 9.4.2.4 2019). NFPA 13 identifies temperature guidance for similar residential heat-producing sources. Sprinklers located 9 to 18 inches from a kitchen range, for instance, should be intermediate-temperature. Sprinklers 18 inches or more away from a kitchen range can be ordinary-temperature. Wall ovens have the same rules. I've often located sprinklers within the center of cooklines as intermediate-temperature sprinklers. This allows a little grace from the edge of heat-producing sources. I'll then check specific appliances for anything that could cause higher temperatures and adjust accordingly. Kitchen hoods that would otherwise form large obstructions can be excluded from sprinkler protection when they contain a separate fire extinguishing system. Consideration #2: Spacing Near Hoods Exhaust hoods are required above cooking equipment that produces grease-laden vapors. NFPA 96 goes further to require that the equipment and exhaust system must also be protected. One way to achieve this requirement is by sprinklers, but this method is rare. Pre-engineered wet chemical systems are designed specifically for cooking hazards. They are also often supplied directly with hood equipment. If a fire extinguishing system is a part of the hood, NFPA 13 relaxes nearby sprinkler protection: NFPA 13 7.10.2.4 (2007-2013), 7.9.2.4 (2016), 8.9.2.3 (2019) Hoods containing automatic fire-extinguishing systems are protected areas; therefore, these hoods are not considered obstructions to overhead sprinkler systems and shall not require floor coverage underneath. NFPA 13 7.10.2.5 (2007-2013), 7.9.2.5 (2016), 8.9.2.4 (2019) Cooking equipment below hoods that contain automatic fire-extinguishing equipment is protected and shall not require protection from the overhead sprinkler system. In regards to sprinkler spacing, the front-edge of a protect exhaust hood is essentially a solid wall. If portions of a hood are not protected, the hood would be considered an obstruction and coverage would need to be provided below the hood. Consideration #3: Obstructions & Conflicts Commercial kitchens are often tightly-designed areas intended to maximize the preparer’s efficiency. End result: high-density of equipment and appliances in small areas. This is the case along the ceiling as well. Lights, diffusers, and sprinklers become secondary and must shift to the narrow remaining ceiling. With hoods and the need for cooling comes large ductwork. These can limit the pipe layout serving sprinklers in kitchens and requires careful coordination. It’s not always easy to tell from plans, but floor-to-ceiling storage is common. Reflected ceiling plans often show a continuous ceiling between one cookline and its adjacent counter. However, there are often heat lamps, pot and pan storage, and a myriad of boxes and other food supplies stored above head height to the ceiling. I try to space sprinklers in these areas directly above walking spaces that can tolerate storage in-between the cooklines. Your Take What has been your experience with suppression systems for commercial kitchens? What challenges have you come across? Let us know here. Find this article helpful? Subscribe to more like this here for free. A little over 3 years ago I started my role in leading a small fire protection group. It is a subset of up to 3 people within a multi-discipline engineering consulting firm. The first week there I asked my boss about what my title should be. He asked what I wanted it to be, largely indifferent to the outcome. If it mattered to me, he said, I should think about it and choose what I feel is right. A myriad of thoughts came to mind. A buddy of mine was just promoted to “Director of Fire Protection Services,” which I liked and sounded fancy. “Team Leader”? Sounded too self-appointed (and too Star-Trek-ian). Finding a Title I asked my wife and it spawned a healthy discussion. A job title should relate to the actual work accomplished so that clients can relate. Sure, that part is easy. Maybe a fancy job title could impact future roles. Maybe a fancy one would make mom proud. After thinking about it for some time I kept asking - does the job title really even matter? I came to this role from a 500+ person company with an assortment of titles and even levels within each title.
At the new small company – what did the title even matter? I’d be doing design, engineering review, business development, project management, and low-level management. The work wouldn’t change whichever title I chose. Sorry, I Still Get Carded It was around that time, just six years into the industry, that a recruiter approached me. It was for a Senior Fire Protection Engineer position. The recruiter said I paired up exactly with the role. He expressed disbelief when I wasn’t interested in the role, considering I was just an Engineer at that time. [side note: I’m somewhat convinced recruiters will say anything to set up a job interview.] Why even have the term “Senior” in a job title if it is even possible for someone 6-years into the industry to have a crack at it? I am not saying I would have gotten the job – I surely would not have – but to even suggest a 29-year old could be a “Senior” Engineer completely degrades the meaning of the term Senior. Perhaps in large organizations the job title is the measure of prestige and responsibility. Perhaps it carries more weight where there is little else to distinguish thousands of employees. But for the rest of the world? The small consultants & contractors? I can’t see it carrying much meaning, or at least nowhere near the importance of the role itself. Your role in fire protection is so much bigger than your job title. Whether you're an intern, engineer, manager, designer, or leader of the multi-hundred-person firm - you play an important role in protecting people and structures from major loss. Your hands create the safety we want to see in the world. That is far more important than your title. Consider your role and your contribution to the world beyond the job title and I promise your work will be more rewarding. So where did I end up with my new job title? I chose “International Director of Fire Protection and Life Safety Design & Consulting Services”. …just kidding, I stuck with “Fire Protection Engineer”. What About You? Where do you stand on job titles? Am I on an island, or have you had similar thoughts yourself? I'm interested in your take - post your thoughts here. p.s. This blog covers weekly takeaways in my experience as a Fire Protection Engineer. Some are thoughts on career while others are real-world technical applications. If you’ve found this interesting, consider sending to a friend. One project question I very commonly receive from civil engineers is whether a post-indicator valve (PIV) is required. In short, there are options. I'm exploring PIVs in more detail in this week's article. If you want to get more like this, subscribe for free here. Purpose of Post-Indicator Valves Post-indicator valves have long been used to stop the flow of water into a building during developed stages of a fire. Exterior wall collapse of a burning building poses a threat to break water supply mains as well as create many openings to the water supply. Without a valve to stop supply to these areas, firefighters and their efforts could be compromised by the loss of pressure and outflow of water to areas of a site that don't need water. With the recognized effectiveness of sprinkler systems and cost pressures, the requirement for post-indicating valves have become more relaxed in the last decade. Code references to account for building collapse, for instance, now appear only indirectly in location requirements for hydrants and post-indicator valves to be sufficiently away from a building. Components of Post-Indicator Valves The post-indicator valve has several important features - first is the ability to quickly shut the valve with use of the post indicator valve handle. The second is to quickly see whether the system is in the 'open' or 'shut' condition in a protected enclosure. It can sometimes be difficult to see after years of dirt on the glass, but not impossible. The valve itself is along the water main below frost depth such that only the stem is subject to freezing conditions. It's a simple concept that's carefully crafted to protect the valve and stem in a reliable fashion. One example of a post-indicating valve - a Mueller Company Vertical Adjustable Post Indicator Valve (see https://www.muellercompany.com/fire-protection/ulfm-indicator-posts/) History of the PIV Requirement So is a post-indicator valve required or not? This used to be an easier question to answer. While not a referenced standard from the International Building Code, the International Fire Code requires that all private fire service mains be installed in accordance with NFPA 24 (IFC 2000-06 Section 508.2.1, 2009-18 507.2.1). NFPA 24, the Standard for the Installation of Private Fire Service Mains and Their Appurtenances, governs system requirements between a water supply main and a building's service entry. Up until the 2010 Edition, NFPA 24 required a listed post indicator valve on every connection from a private fire service main to a building unless special criteria were met (NFPA 24 Section 6.3). The special criteria included the use of a non-indicating underground gate valve with a roadway box and T-wrench or locating an inciating valve in a pit. Either special case required approval of the AHJ. Current Valve Options within NFPA 24 Since the 2010 Edition, NFPA 24 gives a series of options for isolating a building's system and does not mandate that a post-indicator valve be used. These options (from 2010-13 6.2.11, 2016-19 6.2.9) include:
While still considered an "indicating" type valve, wall indicating valves are generally less preferred than post-indicating valves as they are more susceptible to a building collapse than post-indicating valves. Post-Indicator Requirements of NFPA 14 NFPA 14, the Standard for the Installation of Standpipe and Hose Systems, also weighs in on post-indicator valve requirements. NFPA 14 requires that each water supply (except for an FDC) shall be provided with a listed indicating valve in an approved location (NFPA 14 2000 4-2.6.1, 2003-07 6.2.6.1, 2010-19 6.3.6.1.1). The prescriptive way to accomplish this is through the use of a post-indicating valve. Annex material within NFPA 14 goes further, stating a list of preferences for outside control valves:
NFPA 14 does give exceptions (as is almost always the case in fire protection), but they require AHJ-approval. Wall-point-indicating valves, or underground valve with roadway box and T-wrench, are alternative options that require AHJ approval (NFPA 14 2000 4-2.6, 2003-07 6.2.6, 2010-19 6.3.6). Post-Indicator Requirements of NFPA 13 So where does NPFA 13 stand on post-indicator valves? In short, it doesn't. NFPA 13 only states that where post-indicator valves are used, the top of the post must be 32-40 inches above grade, and they must be protected against mechanical damage (NFPA 13 2002 8.15.1.3, 2007-16 8.16.1.3, 2019 16.9.9). AHJ & Insurer Inputs Authorities Having Jurisdiction may also want to weigh in on requirements for post-indicating valves. Some municipalities write code amendments to require PIVs, while others may request PIVs be installed for certain building types. Insurers, such as FM Global, may also want input. FM Global for instance, recommends that each system has a control valve a minimum of 40 feet from the building (with less preferred options also recommended in Data Sheet 2-0 2.6.2). Best Practice What's the best course of action for your project? First, check for local or state code amendments that may affect post-indicating valves. If you have a standpipe system within the building, plan to provide a PIV. Last, check with your AHJ for any nuanced requirements you may be missing or to coordinate a location with the AHJ. Want More? Not already getting these free weekly articles? Subscribe here. Found this helpful? Share on LinkedIn.com or send to a friend. MeyerFire is all about helping you do great work in fire protection with tools, tips and resources. It is a popular and well-established concept that water and electricity don’t mix. Water is electrically conductive which creates a major hazard of electrocution where a continuous pool of water meets a live electrical feed. Can We Omit Sprinklers in Electrical Rooms? On a few occasions I have come across building authorities and building owners who assume that sprinklers will not be installed inside traditional electrical rooms. Why? The basic tenant that water and electricity don’t mix. While the concept is important, the intent of sprinkler protection throughout a building is not just for each item within a building, but the building itself. The primary intent of sprinklers is suppression – or stated differently – to prevent the growth of fire from the room of origin throughout a building. This includes all the rooms and spaces beyond just the electrical room where a fire could begin. This week I’m digging into guidance surrounding electrical rooms. NFPA 13 Guidance
NFPA 13 (2002 Section 8.14.10.3, 2007-10 8.15.10.3, 2013 8.15.11.3, 2016 8.15.11.2, 2019 9.2.6) allows sprinklers to be omitted in electrical rooms, but only where each of the following are met:
Concerns with Providing Sprinklers in Electrical Rooms Providing sprinklers within electrical rooms could:
Historical Approach Prior to the 1994 edition of NFPA 13, important electrical equipment were required to have hoods (or shields) comprised of non-combustible construction to prevent direct contact by sprinkler discharge. All electrical rooms were required to be sprinkler protected. Beginning with the 1994 edition, NFPA 13 introduced language to address concerns for firefighter safety and equipment damage. Sprinklers could be omitted in electrical rooms where the room contains dry-type equipment (no oils), is dedicated to electrical equipment only, is fire-resistant to reduce fire spread, and the room has no storage hazard. The 2016 Edition, the requirement for equipment hoods or shields was removed to direct it under the scope of NFPA 70. Just recently for the 2019 Edition new text was introduced such that no storage is permitted (non-combustible storage had been allowed) and liquid-type K-class (less flammable, non-spreading fluids) would be allowed. International Building Code Input The International Building Code (IBC) does not allow the omission of sprinklers “merely because it is damp, of fire-resistance-rated construction, or contains electrical equipment” (IBC 2000-18 9.3.1.1.1). Within the same code section, the IBC does allow sprinklers to be omitted in “generator and transformer rooms separated from the remainder of the building by walls and floor/ceiling or roof/ceiling assemblies having a fire-resistance rating of not less than 2 hours.” These rooms must have an approved automatic fire detection system. According to IBC commentary, buildings with sprinklers omitted in one of the sections allowed by the IBC would still be considered fully-sprinklered throughout and in compliance with the code and NFPA 13. This distinction is important as it carries eligibility for code alternatives, exceptions and reductions. Today’s Consensus Combined, both the IBC and NFPA 13 require electrical rooms to be protected unless the prescriptive alternative option is followed. As NFPA 13 commentary outlines, sprinkler systems have been successfully installed in rooms containing electrical equipment for over 100 years with no documented instances of a problem. While still seemingly controversial, most projects designed today include sprinkler-protected electrical rooms. Get More If you enjoy these articles, subscribe here. If you're already a subscriber, consider forwarding to a colleague. MeyerFire is all about dissecting real challenges that real people face in fire protection design. I'm thrilled you're a part of our journey for better fire protection worldwide. |
ALL-ACCESSSUBSCRIBEGet Free Articles via Email:
+ Get calculators, tools, resources and articles
+ Get our PDF Flowchart for Canopy & Overhang Requirements instantly + No spam
+ Unsubscribe anytime AUTHORJoe Meyer, PE, is a Fire Protection Engineer out of St. Louis, Missouri who writes & develops resources for Fire Protection Professionals. See bio here: About FILTERS